[TRNSYS-users] HELP making new orientations in type 56
David Bradley
bradley at tess-inc.com
Fri Jul 24 12:17:18 PDT 2009
Marshall,
> I am trying to create a pitched roof for a building (a wall that has a
> slope). I have created two new orientations, NSLOPE and SSLOPE, in
> TRNBUILD. Then I created two new surfaces in the input for weather
> data (type 109). This created 6 new output variables for each of the
> new surfaces. How do I go about connecting these outputs from the
> weather reader to the input of type 56? Can I create a connection
> between the weather reader and the type 56 and connect the variables?
once the new surfaces are defined in Type109, right click on your Type56
in the Studio and tell it to "update building variable list." You should
have three new inputs for each orientation that you defined in TRNBuild.
Then either open an existing connection between Type109 and Type56 or
make a new one and connect the appropriate output and input variables as
you would between any two TRNSYS types.
> Also what are the input variables labeled "CNAT_1" for type 56?
that is not a standard input to Type56 so it pertains to something that
you defined in TRNBuild (or something that was already defined in the
*.bui from which you began). Look through the various managers in
TRNBuild to determine where that input is being used.
> I am also modeling my building with a crawlspace underneath the first
> floor. What is the best way to model the natural earth (dirt) floor
> of the crawl space? Should I create a layer that is similar to rock
> or dirt and declare it as a boundary wall? I've tried using the
> gravel_sand layer from the library and the dirt floor but when I
> declare it as a boundary I always get an error.
The most correct method would be to define a layer of earth (perhaps
10cm of it) as a BOUNDARY wall for the bottom and define whatever the
walls are (concrete perhaps) also as BOUNDARY walls, then connect those
to one of the basement ground coupling models in the TESS Ground
Coupling Library (if you have access to it.) Without that library, you
can use the ASHRAE f-Factor approach to estimating the effective
resistance of the earth but that method is not all that accurate as has
been shown in some recent work by the IEA.
Kind regards,
David
--
***********************************************************************
Thermal Energy System Specialists (TESS), LLC
David BRADLEY 22 N. Carroll Street - Suite 370
Partner Madison, WI 53703
USA
P: +1.608.274.2577
F: +1.608.278.1475
E-mail: bradley at tess-inc.com
Web Pages: http://www.tess-inc.com and http://www.trnsys.com
***********************************************************************
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20090724/99686cd6/attachment-0005.htm>
More information about the TRNSYS-users
mailing list