[TRNSYS-users] Active Layer
Adrien JEZEQUEL - ITF
a.jezequel at itf.biz
Thu Jul 23 05:45:37 PDT 2009
Dear Arnaud,
if you use EXTERNAL category, ambient temperature will be considered on
outside wall surface. /(You can also use BOUNDARY category with external
temperature as input, but wall orientation won't be considered/).
If you want to put ground temperature as external wall temperature, you
may choose "BOUNDARY" in category wall, and define a ground temperature
input (which is defined in Studio)
For information, Type 501 from TESS Library give a Soil Temperature Profile.
Best regards
------------------------------------------------------------------------
www.itf.biz <http://www.itf.biz>
www.itf.biz <http://www.itf.biz>
Adrien JEZEQUEL
Simulations Thermiques Dynamiques
*ITF*
87, Avenue de Chambéry
73230 St Alban Leysse
FRANCE
Phone :
Fax :
Mail:
+33(0) 479 750 029
+33(0) 479 852 122
a.jezequel at itf.biz
/Afin de contribuer au respect de l'environnement, merci de n'imprimer
cet e-mail que si nécessaire
Please, consider our environmental responsability before printing this email
/
A.Thome-08 at student.lboro.ac.uk a écrit :
> Good afternoon everyone,
>
> Within type 56, I have created an active layer which is the ground floor of
> the building I am modelling.
>
> When I define this active layer, in "category", I put "EXTERNAL". Is that
> mean that the software considere that the temperature on the outside
> surface of the layer is the outside ambiante temperature? In this case
> obviously it won't be right because it is not the outside ambiante
> temperature but the ground tempereature which should be defined.
>
> How should I do to model it right? Should I use the category "BOUNDARY"
> instead of "EXTERNAL"? In which case is it clever to use the BOUNDARY
> category?
>
>
> Thank you very much.
>
> Arnaud
>
>
>
>
>
> Arnaud.
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
> ---------------------------------------------------------------------------------------
> Orange vous informe que cet e-mail a ete controle par l'anti-virus mail.
> Aucun virus connu a ce jour par nos services n'a ete detecte.
>
>
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20090723/9d58574f/attachment-0005.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: logo_itf_signature.jpg
Type: image/jpeg
Size: 2884 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20090723/9d58574f/attachment-0005.jpg>
More information about the TRNSYS-users
mailing list