[TRNSYS-users] Heat exchanger temperature control
Mario Leroy Ortiz
ortizm at unm.edu
Thu Jan 15 09:40:38 PST 2009
David,
Sadly, reducing the time step did not fix my problem.
Also, there is plenty of capacitance in the loop as it
has a 30 m3 storage tank and a pipe. I have tried
changing the component order in the control card and in
the loop itself. I have added pipes between the tank and
the pump, the pump and the HX and the HX and the tank. I
have tried making the controlled variable the outlet
temperature out of the HX, the outlet out temperature of a
pump and the outlet temperature of a pipe. Nothing has
given consistent results that I expect, which is for the
cold side pump to mirror/shadow the hot side pump.
I will continue to try other things.
Thank you,
Mario Ortiz
On Wed, 14 Jan 2009 10:01:59 -0600
David Bradley <bradley at tess-inc.com> wrote:
> Mario,
> I have not gotten a chance to look at the attached files
>but chances
> are that there are some convergence problems associated
>with the iterative feedback controller. As I mentioned in
>an email yesterday, the simplifying assumptions that
>often get made in building models of hydronic loop
>components (pumps, heat exchangers, etc.) neglect the
>thermal capacitance of the fluid in the devices, which in
>turn leads to very fast reactions to control decisions.
>In some cases, putting time delays on controllers helps
>solve the convergence problems but often, it just masks
>an underlying issue. My recommendation would be to make
>sure that you have at least one timestep of storage in
>your loop (in other words, model the pipes with some
>realistic thermal losses), reduce the time step and
>tighten the tolerances to at least 0.0001 (the default is
>0.001 I think).
>
> Alternatively, there is a model of a heat exchanger that
>controls the
> outlet temperature using an internal bypass available in
>the TESS Hydronics Library.
> Kind regards,
> David
>
>
> Mario Leroy Ortiz wrote:
>> TESS and TRNSYS users,
>>
>> Please help me with the attached files...
>>
>> I am having some problems controlling the outlet
>>temperature of the
>> cold side of a type 5b counter flow heat exchanger.
>>
>> I am modeling a plate and frame heat exchanger where the
>>heat source
>> is a solar thermal array and the cold side charges a
>>storage tank.
>> Heat is used for a building load.
>>
>> My example project file is simple.
>>
>> Water at a constant temperature (65C) is supplied to a
>>heat exchanger
>> with a varying flow rate (low in morning and afternoon,
>>high at
>> midday) to mimic what might be supplied by a solar
>>array.
>>
>> I am trying to maintain the heat exchanger cold side
>>temperature (tank
>> heat supply) at 60C using a variable speed pump and an
>>iterative
>> feedback controller.
>>
>> Heat is drawn from the tank to the building load.
>>
>> There are 7 days in the simulation. Day 4 and day 7
>>seem to work right.
>>
>> On the other days, during the last hour of time when
>>solar thermally
>> heated water is supplied to the heat exchanger, the cold
>>heat
>> exchanger outlet temperature seems to drop prematurely
>>due to the cold
>> side pump speeding up. Under certain unknown
>>circumstances (days 4
>> and 7), the cold side pump flow mirrors the hot side
>>pump flow and the
>> cold side temperature is maintained for most of the time
>>that solar
>> thermal heat is available. For unknown (to me) reasons,
>>at other
>> times the cold side pump flow is sporadic (speeds up
>>rapidly,
>> decreasing the cold side outlet temperature), especially
>>late in the
>> afternoon.
>>
>> Attached are the project file and input file for my
>>tank.
>>
>> This is an example of the problems I am seeing in a
>>larger project
>> file. This project does not show it, but what I see in
>>the larger
>> project is the cold side pump turning off on me when the
>>hot pump is
>> running at full capacity, causing my solar loop to get
>>very hot.
>>
>> Any assistance with this problem is appreciated.
>>
>> Thank you,
>>
>> Mario Ortiz
>>
>> ------------------------------------------------------------------------
>>
>> _______________________________________________
>> TRNSYS-users mailing list
>> TRNSYS-users at cae.wisc.edu
>> https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
>>
>
> --
> ***********************************************************************
> Thermal Energy System Specialists (TESS), LLC David
>BRADLEY 22 N. Carroll Street - Suite
>370 Partner Madison, WI 53703
> USA
> P: +1.608.274.2577 F: +1.608.278.1475
> E-mail: bradley at tess-inc.com Web Pages:
> http://www.tess-inc.com and
> http://www.trnsys.com
>
> ***********************************************************************
>
More information about the TRNSYS-users
mailing list