[TRNSYS-users] Double skin facade
Monika Schulz
Schulz at transsolar.com
Thu Jan 8 07:19:38 PST 2009
Tiziano,
there are some important points on simulation of a double facade:
- make sure that you have defined the transparent surface between the zones as an adjacent window.
- make reasonable use of the geosurf factor which often is close to 1 if there are big glazing areas.
- note that there is a known issue with the distribution of the diffuse solar radiation to the different surfaces of a zone which is area*absorbtion weighted and thus overestimates solar radiation which is transfered from your gap zone back outside. You should check this (NTYPE73) and if it is too high, give it (partly) back to your zones as a gain. (This issue will be solved in TRNSYS17)
- Make use of the solar balance (NTYPE 901) to check your results.
I hope this helps.
With kind regards
Monika Schulz
TRANSSOLAR Software Team
hotline at transsolar.com <mailto:hotline at transsolar.com>
http://www.trnsys.de/
<http://www.trnsys.de/> http://www.transsolar.com/__software/docs/trnsys/trnsys_uebersicht_de.htm <http://www.transsolar.com/__software/docs/trnsys/trnsys_uebersicht_de.htm>
Transsolar KlimaEngineering - Technologien für energieeffizientes Bauen und Nutzerkomfort in Gebäuden
Transsolar Energietechnik GmbH, Curiestrasse 2, 70563 Stuttgart / Amtsgericht Stuttgart - HRB 23347 / USt-IdNr.: 99073/00911
Geschäftsführer: Dipl.Ing. Matthias Schuler, Dipl.Ing. Thomas Auer, Dipl.Phys. Stefan Holst
_____
Von: Tiziano Terlizzese [mailto:tiziano.terlizzese at mail.ing.unibo.it]
Gesendet: Donnerstag, 8. Januar 2009 09:22
An: TRNSYS-users at cae.wisc.edu
Betreff: [TRNSYS-users] Double skin facade
Hi all,
I'm trying to simulate a double skin facade building. As first step I considered a single office with all the inner walls adiabatic and I divided my model into two zones: the office and the gap between the two panes of the double skin façade. It seems that the solar radiation doesn't reach the office: it doesn't pass through zone 1 (the gap between the panes) into zone 2, the office as it should be. Is there something I need to set?
I'm a beginner, so I thank in advance anybody who can give me some advice.
Tiziano Terlizzese
PhD student
Università di Bologna
DIENCA