[TRNSYS-users] Type 109 vs type 15
Maarten Sourbron
Maarten.Sourbron at mech.kuleuven.be
Wed Feb 11 02:29:43 PST 2009
Dear Trnsys-users,
For an analysis of Belgium weather data, I constructed weather files
using the Trnsys type 109 and 15 and the meteonorm file for Uccle,
Belgium. Making a summation of the resulting radiation on vertical
planes facing N, E, S and W, I notices big differences. The table below
indicates this :
T-drybulb I_tot_hor-1
I_tot_hor-2
I_tot_N
I_tot_E
I_tot_S
I_tot_W
Datareader 15-6 9,73 3416548 3416548 2302065 3075940 3625084 3081463
Datareader 109 9,73 3416548 3416296 1192961 2087489 2720244 2076203
Datareader 15-2 9,73 3416548 3416548 2302065 3075940 3625084 3081463
Difference 15vs109 -5,91E-05 0,088266 251,4136 1109105 988451
904839,9 1005260
0,00% 0,00% 0,01% 48,18% 32,13% 24,96% 32,62%
The two horizontal radiation values are : 1)directly provided by the
weather file and 2)processed using a plane with slope 0°
Am I doing something obvious wrong? Because the results are cearly too
different to be acceptable.
The dck files is included.
Many thanks,
Maarten Sourbron
--
Departement Werktuigkunde-Department of Mechanical Engineering
Katholieke Universiteit Leuven
Celestijnenlaan 300A bus 2421
3001 Heverlee (Leuven)
T : 0032 (0)16 32 28 73
F : 0032 (0)16 32 29 85
E : Maarten.Sourbron at mech.kuleuven.be
Disclaimer: http://www.kuleuven.be/cwis/email_disclaimer.htm
-------------- next part --------------
VERSION 16.1
*******************************************************************************
*** TRNSYS input file (deck) generated by TrnsysStudio
*** on woensdag, februari 11, 2009 at 11:27
*** from TrnsysStudio project: \\mech.kuleuven.be\homes\sourbron\Doctoraat\Modellen\Data\Weather.tpf
***
*** If you edit this file, use the File/Import TRNSYS Input File function in
*** TrnsysStudio to update the project.
***
*** If you have problems, questions or suggestions please contact your local
*** TRNSYS distributor or mailto:software at cstb.fr
***
*******************************************************************************
*******************************************************************************
*** Units
*******************************************************************************
*******************************************************************************
*** Control cards
*******************************************************************************
* START, STOP and STEP
CONSTANTS 3
START=0
STOP=8760
STEP=1
* User defined CONSTANTS
SIMULATION START STOP STEP ! Start time End time Time step
TOLERANCES 0.001 0.001 ! Integration Convergence
LIMITS 30 30 30 ! Max iterations Max warnings Trace limit
DFQ 1 ! TRNSYS numerical integration solver method
WIDTH 80 ! TRNSYS output file width, number of characters
LIST ! NOLIST statement
! MAP statement
SOLVER 0 1 1 ! Solver statement Minimum relaxation factor Maximum relaxation factor
NAN_CHECK 0 ! Nan DEBUG statement
OVERWRITE_CHECK 0 ! Overwrite DEBUG statement
TIME_REPORT 0 ! disable time report
EQSOLVER 0 ! EQUATION SOLVER statement
* Model "Type15-6" (Type 15)
*
UNIT 6 TYPE 15 Type15-6
*$UNIT_NAME Type15-6
*$MODEL .\Weather Data Reading and Processing\Standard Format\Meteonorm Files (TM2)\Type15-6.tmf
*$POSITION 215 213
*$LAYER Main #
PARAMETERS 21
6 ! 1 File Type
54 ! 2 Logical unit
3 ! 3 Tilted Surface Radiation Mode
0.2 ! 4 Ground reflectance - no snow
0.7 ! 5 Ground reflectance - snow cover
5 ! 6 Number of surfaces
1 ! 7 Tracking mode-1
0 ! 8 Slope of surface-1
0 ! 9 Azimuth of surface-1
1 ! 10 Tracking mode-2
90 ! 11 Slope of surface-2
180 ! 12 Azimuth of surface-2
1 ! 13 Tracking mode-3
90 ! 14 Slope of surface-3
-90 ! 15 Azimuth of surface-3
1 ! 16 Tracking mode-4
90 ! 17 Slope of surface-4
0 ! 18 Azimuth of surface-4
1 ! 19 Tracking mode-5
90 ! 20 Slope of surface-5
90 ! 21 Azimuth of surface-5
*** External files
ASSIGN "C:\Program Files\Trnsys16_1\Weather\Meteonorm\Europe\BE-Uccle-64470.tm2" 54
*|? Which file contains the Meteonorm weather data? |1000
*------------------------------------------------------------------------------
* Model "Type109-TMY2" (Type 109)
*
UNIT 4 TYPE 109 Type109-TMY2
*$UNIT_NAME Type109-TMY2
*$MODEL .\Weather Data Reading and Processing\Standard Format\TMY2\Type109-TMY2.tmf
*$POSITION 212 349
*$LAYER Weather - Data Files #
PARAMETERS 4
2 ! 1 Data Reader Mode
57 ! 2 Logical unit
4 ! 3 Sky model for diffuse radiation
1 ! 4 Tracking mode
INPUTS 11
0,0 ! [unconnected] Ground reflectance
0,0 ! [unconnected] Slope of surface-1
0,0 ! [unconnected] Azimuth of surface-1
0,0 ! [unconnected] Slope of surface-2
0,0 ! [unconnected] Azimuth of surface-2
0,0 ! [unconnected] Slope of surface-3
0,0 ! [unconnected] Azimuth of surface-3
0,0 ! [unconnected] Slope of surface-4
0,0 ! [unconnected] Azimuth of surface-4
0,0 ! [unconnected] Slope of surface-5
0,0 ! [unconnected] Azimuth of surface-5
*** INITIAL INPUT VALUES
0.2 0.0 0.0 90 180 90 270 90 0 90 90
*** External files
ASSIGN "C:\Program Files\Trnsys16_1\Weather\Meteonorm\Europe\BE-Uccle-64470.tm2" 57
*|? Weather data file |1000
*------------------------------------------------------------------------------
* Model "Type15-2" (Type 15)
*
UNIT 8 TYPE 15 Type15-2
*$UNIT_NAME Type15-2
*$MODEL \Program Files\Trnsys16_1\Studio\Proformas\Weather Data Reading and Processing\Standard Format\TMY2\Type15-2.tmf
*$POSITION 206 509
*$LAYER Weather - Data Files #
PARAMETERS 21
2 ! 1 File Type
65 ! 2 Logical unit
3 ! 3 Tilted Surface Radiation Mode
0.2 ! 4 Ground reflectance - no snow
0.7 ! 5 Ground reflectance - snow cover
5 ! 6 Number of surfaces
1 ! 7 Tracking mode-1
0 ! 8 Slope of surface-1
0 ! 9 Azimuth of surface-1
1 ! 10 Tracking mode-2
90 ! 11 Slope of surface-2
180 ! 12 Azimuth of surface-2
1 ! 13 Tracking mode-3
90 ! 14 Slope of surface-3
-90 ! 15 Azimuth of surface-3
1 ! 16 Tracking mode-4
90 ! 17 Slope of surface-4
0 ! 18 Azimuth of surface-4
1 ! 19 Tracking mode-5
90 ! 20 Slope of surface-5
90 ! 21 Azimuth of surface-5
*** External files
ASSIGN "C:\Program Files\Trnsys16_1\Weather\Meteonorm\Europe\BE-Uccle-64470.tm2" 65
*|? Which file contains the TMY-2 weather data? |1000
*------------------------------------------------------------------------------
* Model "Type25a" (Type 25)
*
UNIT 5 TYPE 25 Type25a
*$UNIT_NAME Type25a
*$MODEL .\Output\Printer\Unformatted\TRNSYS-Supplied Units\Type25a.tmf
*$POSITION 437 181
*$LAYER Outputs #
PARAMETERS 10
STEP ! 1 Printing interval
START ! 2 Start time
STOP ! 3 Stop time
59 ! 4 Logical unit
2 ! 5 Units printing mode
0 ! 6 Relative or absolute start time
-1 ! 7 Overwrite or Append
-1 ! 8 Print header
0 ! 9 Delimiter
1 ! 10 Print labels
INPUTS 9
6,1 ! Type15-6:Dry bulb temperature ->Input to be printed-1
6,11 ! Type15-6:Total sky cover ->Input to be printed-2
6,14 ! Type15-6:Global horizontal radiation (not interpolated) ->Input to be printed-3
6,18 ! Type15-6:Total horizontal radiation ->Input to be printed-4
6,24 ! Type15-6:Total tilted surface radiation for surface-1 ->Input to be printed-5
6,25 ! Type15-6:Total tilted surface radiation for surface-2 ->Input to be printed-6
6,26 ! Type15-6:Total tilted surface radiation for surface-3 ->Input to be printed-7
6,27 ! Type15-6:Total tilted surface radiation for surface-4 ->Input to be printed-8
6,28 ! Type15-6:Total tilted surface radiation for surface-5 ->Input to be printed-9
*** INITIAL INPUT VALUES
T-drybulb Total_sky_cover I_tot_hor(not-int) I_tot_hor-2 I_tot_hor-3
I_tot_N I_tot_E I_tot_S I_tot_W
*** External files
ASSIGN "BE-Uccle-64470-1.out" 59
*|? Output File for printed results |1000
*------------------------------------------------------------------------------
* Model "Type25a-2" (Type 25)
*
UNIT 7 TYPE 25 Type25a-2
*$UNIT_NAME Type25a-2
*$MODEL .\Output\Printer\Unformatted\TRNSYS-Supplied Units\Type25a.tmf
*$POSITION 438 338
*$LAYER Main #
PARAMETERS 10
STEP ! 1 Printing interval
START ! 2 Start time
STOP ! 3 Stop time
60 ! 4 Logical unit
2 ! 5 Units printing mode
0 ! 6 Relative or absolute start time
-1 ! 7 Overwrite or Append
-1 ! 8 Print header
0 ! 9 Delimiter
1 ! 10 Print labels
INPUTS 9
4,1 ! Type109-TMY2:Ambient temperature ->Input to be printed-1
0,0 ! [unconnected] Input to be printed-2
4,9 ! Type109-TMY2:extraterrestrial radiation on horizontal ->Input to be printed-3
4,12 ! Type109-TMY2:total radiation on horizontal ->Input to be printed-4
4,18 ! Type109-TMY2:total radiation on tilted surface-1 ->Input to be printed-5
4,24 ! Type109-TMY2:total radiation on tilted surface-2 ->Input to be printed-6
4,30 ! Type109-TMY2:total radiation on tilted surface-3 ->Input to be printed-7
4,36 ! Type109-TMY2:total radiation on tilted surface-4 ->Input to be printed-8
4,42 ! Type109-TMY2:total radiation on tilted surface-5 ->Input to be printed-9
*** INITIAL INPUT VALUES
T-drybulb Total_sky_cover I_extraterra I_tot_hor-2 I_tot_hor-3 I_tot_N
I_tot_E I_tot_S I_tot_W
*** External files
ASSIGN "BE-Uccle-64470-2.out" 60
*|? Output File for printed results |1000
*------------------------------------------------------------------------------
* Model "Type25a-3" (Type 25)
*
UNIT 10 TYPE 25 Type25a-3
*$UNIT_NAME Type25a-3
*$MODEL .\Output\Printer\Unformatted\TRNSYS-Supplied Units\Type25a.tmf
*$POSITION 426 491
*$LAYER Main #
PARAMETERS 10
STEP ! 1 Printing interval
START ! 2 Start time
STOP ! 3 Stop time
63 ! 4 Logical unit
2 ! 5 Units printing mode
0 ! 6 Relative or absolute start time
-1 ! 7 Overwrite or Append
-1 ! 8 Print header
0 ! 9 Delimiter
1 ! 10 Print labels
INPUTS 9
8,1 ! Type15-2:Dry bulb temperature ->Input to be printed-1
8,11 ! Type15-2:Total sky cover ->Input to be printed-2
8,14 ! Type15-2:Global horizontal radiation (not interpolated) ->Input to be printed-3
8,18 ! Type15-2:Total horizontal radiation ->Input to be printed-4
8,24 ! Type15-2:Total tilted surface radiation for surface-1 ->Input to be printed-5
8,25 ! Type15-2:Total tilted surface radiation for surface-2 ->Input to be printed-6
8,26 ! Type15-2:Total tilted surface radiation for surface-3 ->Input to be printed-7
8,27 ! Type15-2:Total tilted surface radiation for surface-4 ->Input to be printed-8
8,28 ! Type15-2:Total tilted surface radiation for surface-5 ->Input to be printed-9
*** INITIAL INPUT VALUES
T-drybulb Total_sky_cover I_tot_hor(not-int) I_tot_hor-2 I_tot_hor-3
I_tot_N I_tot_E I_tot_S I_tot_W
*** External files
ASSIGN "BE-Uccle-64470-3.out" 63
*|? Output File for printed results |1000
*------------------------------------------------------------------------------
END