Carolina,
Type2 models a controller that only has an ON and and OFF position. As
soon as the pump turns on, it outputs its full flow. If you need a pump
whose flow will vary, you need to use a controller (or an equation) that
generates a signal between 0 and 1 that is proportional to the speed at
which you want to run the pump.
Kind regards,
David
Carolina Belli wrote:
>
> Hi,I'm a new user of TRNSYS, for my thesis
>
>
>
> I have to simulate a solar desalination plant. For the solar collector
> I use type 73 (flate plate), but I have a problem with the value of
> the T out: it reach above 100°C.
>
> The solar circuit is: flat plate collector (type 73) -- storage tank
> (type 4e) -- single variable pump. There is also a controller (type
> 2b) to control the on/off of the pump. I connect the Th of type 2b
> with Tout of the collector, and Tl of type 2b with the Tout of the
> storage tank. The problem is when the pump have to start or to stop:
> the flow rate rapidly increase/ decrease from 0 to the set value (and
> vice versa).
>
> I try to decrease the flow through the collector but I can't manage to
> solve the problem of the Tout of the panel.
>
>
>
> With many thanks,
>
>
>
> Carolina
>
>
>
>
>
> ------------------------------------------------------------------------
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
>
--
***********************************************************************
Thermal Energy System Specialists (TESS), LLC
David BRADLEY 22 N. Carroll Street - Suite 370
Partner Madison, WI 53703
USA
P: +1.608.274.2577
F: +1.608.278.1475
E-mail: bradley at tess-inc.com
Web Pages: http://www.tess-inc.com and http://www.trnsys.com
***********************************************************************
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20090211/a437eee5/attachment-0001.htm>
More information about the TRNSYS-users
mailing list