[TRNSYS-users] Coupling airflow (in TRNbuild) versus TRNflow
David Bradley
bradley at tess-inc.com
Tue Feb 10 09:57:39 PST 2009
Kevin,
TRNBuild (Type56) only asks the user to provide the amount of air flow
from zone "A" into zone "B" (note that Type56 does NOT assume that an
equal amount of air flows back from zone "B" to zone "A" so you have to
take care of the mass balance manually). TRNFlow actually figures out
what the flows back and forth would be based on temperature differences,
pressure differences, and mechanical systems in the two zones. It also
takes into account the entire building, not just the two zones. I
imagine that it would be very hard to run exactly the same case using
TRNBuild and setting the mass flows manually and using TRNFlow. Even if
the flow between the two zones is the same, it may be that TRNFlow is
calculating some other flows elsewhere (increased infiltration for example).
Kind regards,
David
kevin maiques wrote:
>
> Dear TRNsys-users
>
> I simulate the same flow between two zones with TRNbuild and TRNflow.
> But I don't have same results.
> It seems to me that the evolution of temperature is more realistic
> than temperature with coupling airflow of TNRbuild.
>
> I want to know ifI can continue to simulate coupling airflow with
> TRNbuild or not?
>
> Best Regards.
>
> ------------------------------------------------------------------------
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
>
--
***********************************************************************
Thermal Energy System Specialists (TESS), LLC
David BRADLEY 22 N. Carroll Street - Suite 370
Partner Madison, WI 53703
USA
P: +1.608.274.2577
F: +1.608.278.1475
E-mail: bradley at tess-inc.com
Web Pages: http://www.tess-inc.com and http://www.trnsys.com
***********************************************************************
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20090210/7e0a804f/attachment-0001.htm>
More information about the TRNSYS-users
mailing list