[TRNSYS-users] turn
David Bradley
bradley at tess-inc.com
Mon Feb 2 08:39:43 PST 2009
Kiki,
The Type67 data file surface angles for which obstruction heights are
provided correspond to absolute azimuths. They are not specified
relative to the azimuth of the opening. If you want to turn your
building, you need apply the same turn in the Type67 data file. The
"turn" equation only turns the building itself, not its surroundings.
Kind regards,
David
kiki siouna wrote:
> */Thank you.
> I have one more question. In my simulation for the shading of the
> building from the surrounding buildings i used type 67. Now i want to
> turn the building, so i change the azimuth of surfaces in the equation
> 'turn'. With this, i turn only the simulated building or the hole
> system( simulated building and surroundings).
> Thank you for your help./*
>
> ------------------------------------------------------------------------
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
>
--
***********************************************************************
Thermal Energy System Specialists (TESS), LLC
David BRADLEY 22 N. Carroll Street - Suite 370
Partner Madison, WI 53703
USA
P: +1.608.274.2577
F: +1.608.278.1475
E-mail: bradley at tess-inc.com
Web Pages: http://www.tess-inc.com and http://www.trnsys.com
***********************************************************************
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20090202/2a9e55f2/attachment-0001.htm>
More information about the TRNSYS-users
mailing list