Feargal,
The description of that Type can be found in the ..\Trnsys16_1\Tess 
Models\Documentation\Applications Library\ directory. Essentially it has 
two outputs, one for "heating allowed" and one for "cooling allowed." To 
set up the component, click on the plugin icon at the bottom left of the 
proforma (see other threads if you have trouble doing this). The 
component outputs a "1" for the "heating allowed" output if the 
simulation time is within the defined heating season. Likewise, it 
outputs a "1" for the "cooling allowed" output if the simulation is 
within the defined cooling season. The outputs can be used as 
multipliers on other control signals to equipment that should be 
switched off during part of the year.
Kind regards,
David