Hi Marina,
I think the problem is that the temperature changes because of the air flow in the church, not because of convection between walls (even 0 cm size). Per default, there is no air flow between zones - you have to define them.
To do that, you may have to use a component like CONTAM (type 93) or COMIS (type 157).
Werner
________________________________
De : Marina Fehl [mailto:marinafehl at gmx.de]
Envoyé : mercredi 5 août 2009 20:54
À : trnsys-users at engr.wisc.edu
Objet : [TRNSYS-users] church
hi TRNSYS users,
I try to simulate a temperature distribution in a church. I tried to devide the volume into many parts with adjacent walls which consist of 0,00m air only. However, I´sure it isolate as well. Is there another way? Is there may be a special tool to simulate the temperature distribution in a huge room, a specially in vertical levels.
thank you for help