I'd recommend that you define an equation in your input file that has a
value of 1 if the hour of the year (built-in variable "TIME") is less
than (for example) 2500 or greater than 4500 and zero otherwise. You can
use the BOOLEAN functions GT() and LT() to accomplish this. The result
of the equation should be multiplied by the control signal of your Type2
before being sent to the heat pumps. You could also use Type515 (Heating
and Cooling Season Scheduler) if you have access to the TESS
Applications library.
Kind Regards,
David
Ludivine Fogolin wrote:
> hello,
> I installed a heat pump in my simulation, it works with a floor
> heating at the ground floor.
> How can I make so that it does not function in summer?
> For the moment considering the inertia of my floor, it turns all the
> year because I knew to put only one regulation on the fact that it
> arrète to turn itself when the interior temperature is higher than
> 22°C (that thanks to a system of the 2b type)
> What would I like to know it is if it is possible to spend the same
> omment kind of system but this time to say to him that it cannot
> déclancher if one is between on June 1 and on August 31?
> One also spoke to me to put a computer to make him do it OFF ONE, but
> I really do not see how!!!!
> Could you say to me how I must make?
> In advance thank you
> Ludivine
>
> ------------------------------------------------------------------------
> 250 photos de vacances à partager ? Ca risque de ne pas passer par
> e-mail, mais bien sur Windows Live Photos.
> <http://www.microsoft.com/belux/fr/windows/windowslive/products/photos.aspx>
>
> ------------------------------------------------------------------------
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
>
--
***********************************************************************
Thermal Energy System Specialists (TESS), LLC
David BRADLEY 22 N. Carroll Street - Suite 370
Partner Madison, WI 53703
USA
P: +1.608.274.2577
F: +1.608.278.1475
E-mail: bradley at tess-inc.com
Web Pages: http://www.tess-inc.com and http://www.trnsys.com
***********************************************************************
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20090817/d586e103/attachment-0001.htm>
More information about the TRNSYS-users
mailing list