[TRNSYS-users] Question
David Bradley
bradley at tess-inc.com
Thu Aug 20 13:46:25 PDT 2009
Senne,
Typically the way this would be accomplished is to connect the flow
from Type60's outlet to the active layer fluid inlet temperature and
mass flow rate via a pump and to turn the pump on and off based on the
control signal of a thermostat that watches the zone temperature
(Type108 would be a good choice for the thermostat model). The tank
would then be kept warm separately by some kind of heater. Type60 has a
thermostat and heater built into it if you want to use an electric or
gas element. Take a look at parameters 15 through 29. If you are heating
the tank by external means (a solar collector, a heat pump, etc.) then
Type2 is probably the correct choice but it should look at the tank
bottom temperature and the outlet temperature of the heating device.
Kind regards,
David
senne plessers wrote:
> Dear all,
>
> I recently start using trnsys16, now I have to implement a house that has
> an active layer in the floor and in the ceiling. To supply the heating
> I added
> a thermal storage (type60t) that is connected to the actieve layer and the
> heating in trnbuild.
>
> Now I want to control this heating or storage tank, I want to turn off
> the heating
> when the temperature rises above a certain value, because above this
> value it is
> not necessary to produce heat. I thought I had to do it with type2 but
> it doesn't
> seem to work. Is there a way to shut the heating off in these periods?
> Or am I
> doing something wrong with my parameters and inputs? I follow this
> procedure:
>
> Upper input temperature=25
> Lower input temperature I connect with the temperature of a thermal zone
> Monitoring temperature=0
> Upper dead band = 5
> Lower dead band=0
> The output control function I connect with the input of the heating
>
>
> Kind Regards,
>
> Senne
>
> ------------------------------------------------------------------------
> Je hele online leven op één stek? Ontdek Windows Live!
> <http://www.microsoft.com/belux/nl/windows/windowslive/default.aspx>
> ------------------------------------------------------------------------
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
>
--
***********************************************************************
Thermal Energy System Specialists (TESS), LLC
David BRADLEY 22 N. Carroll Street - Suite 370
Partner Madison, WI 53703
USA
P: +1.608.274.2577
F: +1.608.278.1475
E-mail: bradley at tess-inc.com
Web Pages: http://www.tess-inc.com and http://www.trnsys.com
***********************************************************************
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20090820/ae1ba1e3/attachment.htm>
More information about the TRNSYS-users
mailing list