I would think that all you would need would be Type56 and Type109
(plus Type33 and Type69 I think). You can just set the cooling
temperature in your zones to 24.2C and allow the cooling equipment to
have unlimited power, then take a look at the maximum cooling load that
was required. That should give you the required system size. Keep in
mind three things:
1. Type109 reads a typical (average) weather year file - not an extreme
one and typically (right or wrong) system sizing is done based on a
worst-case scenario, not on an average year.
2. If you plan for your lab to have temperature setups and setbacks,
your max cooling load will be enormous because technically the load is
infinite when your set point temperature comes back from its set up
condition. I would recommend using a constant setpoint in order to find
your system size.
3. The Type56 output QSENS is sensible cooling only! In order to get a
latent component, you must also impose an RH setpoint on the zone and
look at the QLAT output from Type56. This isn't ideal because often the
latent cooling is an effect of the sensible cooling (not something that
can be controlled separately). We wrote a component based on some curve
fits that calculate the amount of latent cooling that a "cooling coil
type" of cooling device can do based on zone temperature and ambient wet
bulb (If I am remembering correctly). Its latent cooling ability turns
into a negative moisture gain on the space, which is fed back to Type56.
The component will be part of the TESSLibs 3.0 but for the moment is an
individual component.
Kind regards,
David
Sebastian Schlott wrote:
> My Problem,
>
> I have 2 rooms, used as a lab.
>
> In this rooms there is a thermal load of 15kw which has to be cooled away.
>
> The ambition is the simulation of the room temperature.
> Target: 24°C +- 0,2 °C
> Question: Is the installed system strong enough, which systempower do I need?
>
> At the moment the installed system has not the ability to cool 15 kw away.
>
> is it enough to use the build (type56) and weather data(Type109) to simulate this situation?
>
> Mit freundlichem Gruß
>
> i. A. Sebastian Schlott
>
>
> ------------------------------------
> Kuehn Bauer Partner
> Beratende Ingenieure GmbH
> Wilhelm-Wagenfeld-Strasse 6
> 80807 München
>
> T: +49 89 189 16-182
> F: +49 89 189 16-110
> E: ses at kbp.de
>
> Geschäftsführung: Michael Kuehn jr.
> HRB 102024
> ------------------------------------
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
>
>
>
>
--
***********************************************************************
Thermal Energy System Specialists (TESS), LLC
David BRADLEY 22 N. Carroll Street - Suite 370
Partner Madison, WI 53703
USA
P: +1.608.274.2577
F: +1.608.278.1475
E-mail: bradley at tess-inc.com
Web Pages: http://www.tess-inc.com and http://www.trnsys.com
***********************************************************************
More information about the TRNSYS-users
mailing list