[TRNSYS-users] sky temp (type 69) inconsistent inputs warning
    Timothy McDowell 
    mcdowell at tess-inc.com
       
    Mon Apr 13 14:50:33 PDT 2009
    
    
  
Cramer -
I have seen this when the weather file is 'missing' cloud cover data -
meaning that there are 99s entered in the data for some hours.  Type69
checks this and flags it as being greater than 1.
Tim
----------------------------------
Timothy McDowell
Executive Vice President
Thermal Energy System Specialists, LLC
22 N. Carroll St, Suite 370
Madison, WI 53703
Phone: 608-274-2577
Fax: 608-278-1475
----- Original Message -----
From: "Cramer Silkworth" <silkworth at transsolar.com>
Sent: Mon, April 13, 2009 13:55
Subject:[TRNSYS-users] sky temp (type 69) inconsistent inputs warning
Hi
All,
I'm getting an
annoying but work-aroundable error, but I'm curious see if there's a real
problem. When running a simple deck file to create a climate analysis (no
building, just radiations & temps, etc), I get a bunch of the below
warnings, ultimately maxing out and causing a fatal error. I can get past
it by
increasing my max warnings, but I'm curious what the real issue is. I've
checked
for the things it says in the message but none of those conditions exists.
Anybody got any ideas? Or does type 69 just get cranky easily?
*** Warning at
time       :
584.000000
    Generated by Unit
:    69
    Generated by
Type     :    69
    TRNSYS
Message    317 : The sky temperature model has reported an
inconsistency in the supplied INPUTS. The inconsistency has been fixed but
should be investigated as it may lead to other problems. This error can be
caused by a dew point temperature above the ambient temperature, a solar
radiation value less than zero, or a cloud cover fraction less than zero or
greater than one
    Reported information  : Not
available
Thanks,
-Cramer
J. Cramer Silkworth
Transsolar Inc.
Technical
consulting for energy efficiency and user comfort in buildings. Stuttgart -
Munich - New York
134 Spring Street Suite 601
New York, NY 10012
212-219-2255
silkworth at transsolar.com
_______________________________________________
TRNSYS-users mailing list
TRNSYS-users at cae.wisc.edu
https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
----- End of original message -----
    
    
More information about the TRNSYS-users
mailing list