Hallo Jerome!

If You're only interested in the better part of the sum of all rooms You can just simulate a single room and set the boundary-condition to identical. Then You can scale the results; For example heating-energy-demand x200, ...

If You also want to analyse the rooms under the roof and in the corners of the building, You should simulate at least two moor room additional to the centre of the building (roof-room + 2 not-roof-room).

The simulation-method was developed and proven by Prof. Gerd Hauser (*1).

Regards,
	Matthias Kersken



(*1): 
Hauser, G.:
Vereinfachte Behandlung  des Wärmeverhaltens großer Gebäude durch thermische Systeme /
Simplified treatment of calorific values of large buildings by approximation of thermal Systems /
Traitement slmpllfie de la calorimetrie de grands immeubles par approximation de systemes thermiques
BETONWERK + FERTIGTEIL-TECHNIK, HEFT 5, (1978).

---
 
Dipl.-Ing. Matthias Kersken
Wissenschaftlicher Mitarbeiter / Abteilung Energiesysteme


Fraunhofer-Institut für Bauphysik 
Institutsteil Holzkirchen

Fraunhoferstraße 10
83626 Valley

eMail: Matthias.Kersken at ibp.fraunhofer.de
Telefon 08024 / 643-204
Telefax 08024 / 643-366
www.ibp.fraunhofer.de

Dipl.-Ing. Matthias Kersken
Research Associate / Department Energy Systems 

Fraunhofer Institute for Building Physics 
Branch Holzkirchen

Fraunhoferstraße 10
83626 Valley

eMail: Matthias.Kersken at ibp.fraunhofer.de
Phone +49 8024 / 643-204
Fax +49 8024 / 643-366
www.ibp.fraunhofer.de


-----Ursprüngliche Nachricht-----
Von: Sebbag Jerome [mailto:jerome.sebbag at insa-lyon.fr] 
Gesendet: Samstag, 4. April 2009 11:43
An: trnsys-users at cae.wisc.edu
Betreff: [TRNSYS-users] Simulate a 4-storey building with identical zones


Hi everyone,

I am simulating a 4-storey hotel (200 rooms), with TRNBUILD. All the rooms are identical, with identical thermal behaviour. Do I have to create 200 zones, or can I simplify the model?
Thank you in advance!

Jerome







More information about the TRNSYS-users mailing list