[TRNSYS-users] Simulate a 4-storey building with identical zones

David Bradley bradley at tess-inc.com
Mon Apr 6 13:37:36 PDT 2009


Jerome,
  I would definitely recommend simplifying the model. If multiple rooms 
are served by the same HVAC system (a variable air volume system for 
example) then I would put all of the rooms that are served by a single 
air handler and that are on a given floor together into one thermal 
zone. If all the rooms are on their own system (a packaged terminal air 
conditioner for example) then you only have to model the rooms that have 
a distinct configuration (ie one on each corner of the ground floor, one 
along each length wall of the ground floor, one on each corner of a 
typical middle floor, one in the middle of each wall on a middle floor, 
one on each corner of the top floor, one along each wall of the top 
floor and then all of the special zones (breakfast room, corridor, 
laundry facility, etc.)
Kind regards,
 David


Sebbag Jerome wrote:
> Hi everyone,
>
> I am simulating a 4-storey hotel (200 rooms), with TRNBUILD. All the  
> rooms are identical, with identical thermal behaviour. Do I have to  
> create 200 zones, or can I simplify the model?
> Thank you in advance!
>
> Jerome
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
>
>
>
>   

-- 
***********************************************************************
Thermal Energy System Specialists (TESS), LLC 
David BRADLEY                      22 N. Carroll Street - Suite 370 
Partner                            Madison, WI 53703 
                                   USA
P: +1.608.274.2577 
F: +1.608.278.1475
E-mail: bradley at tess-inc.com 
Web Pages:  http://www.tess-inc.com    and      http://www.trnsys.com

***********************************************************************




More information about the TRNSYS-users mailing list