Ordoumpozanis Konstantinos,
  If the simulation begins to have problems at very high flow rates, 
check to make sure that there is actually enough pipe volume in your 
system to contain the amount of fluid that you are trying to pump. You 
will probably have to decrease the time step, increase the size of the 
bore field, perhaps add or increase the size of the pipes that lead from 
the heat pump to the field, and perhaps increase the size of the heat 
pump itself as well.
Kind regards,
 David
Ordoumpozanis Konstantinos wrote:
>
> Hi
>
> I am trying to run an application in geothermal heat pump, with the 
> pre-installed module of the tess libraries (without the vertical 
> tubes) and I have noticed the with high flow values (over 8000 kg/h) i 
> have an error "overflow stack". But generally i canot be sure if the 
> results that i get are correct, because i am very new to geothermal 
> heat pumps..
>
> Could anyone help me with the error that I get, and suggest me a way 
> to run a correct case ?
>
>
> thank you
>
> ------------------------------------------------------------------------
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
>   
-- 
***********************************************************************
Thermal Energy System Specialists (TESS), LLC 
David BRADLEY                      2916 Marketplace Drive - Suite 104 
Partner                            Madison, WI 53719 
                                   USA
P: +1.608.274.2577 
F: +1.608.278.1475
E-mail: bradley at tess-inc.com 
Web Pages:  http://www.tess-inc.com    and      http://www.trnsys.com
***********************************************************************
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20080912/00e6d171/attachment-0005.htm>
    
    
More information about the TRNSYS-users
mailing list