[TRNSYS-users] Modelling a greenhouse using Type 56
knut.erik.enerstvedt at niva.no
knut.erik.enerstvedt at niva.no
Thu Oct 30 07:56:30 PDT 2008
David,
Thanks again for a thorough answer.
I have some more questions related to the same topic:
I wish to model a greenhouse with sloped roof and more than one top. In
Type 56, will adding one wall tilted in the first direction (upward slope)
and a second wall tilted in the other direction (downward slope) have the
same effect as adding several walls in both directions, as long as the
surface area matches?
I usually set geosurf to zero for all surfaces to keep things simple. Do
you think this is acceptable for a greenhouse?
What do you think the thernal capacitance should be in a greenhouse (upper
and lower zones)?
Thanks again and kind regards,
Knut Erik
David Bradley
<bradley at tess-inc
.com> To
knut.erik.enerstvedt at niva.no
29.10.2008 18:08 cc
Subject
Re: [TRNSYS-users] Modelling a
thermal screen/horizontal shade in
a Type 56 greenhouse
Knut Erik,
I think your approach is good. The one thing that you have to keep in
mind is that with CONTAM (or COMIS / TRNFlow), the flow through a
horizontal opening is uni-directional because it is driven by a pressure
difference and a temperature difference. Those flow paths do not have an
ability to show an updraft in the middle of a zone and a downdraft at
the perimeter. This can lead to a non-convergent solution in CONTAM.
Sometimes you have to artificially restrict the effective size of the
horizontal opening to prevent too large a volume of air from going from
one zone to the other. I have talked to the CONTAM developers about the
problem and how best to try and solve it but we have never come up with
a very good verdict.
Kind regards,
David
PS: hopefully, Transsolar will answer the question about the NTYPE...
those confuse me terribly and I don't want to tell you something that is
incorrect!
knut.erik.enerstvedt at niva.no wrote:
> Dear TRNSYS users,
>
> I am trying to model a greenhouse with a thermal screen using Type 56.
The
> greenhouse consists of two zones, one above and one below, with the
screen
> as a horizontal shade between the zones. My plan to model the screen is
to
> define an ADJACENT window between the upper and lower zone, choose a
window
> with no glazing (non-existant or open) and have an internal shading
device
> controlled by an input variable. I will also use CONTAM to calculate the
> air exchange between the two zones.
>
> Can anyone tell me if this approach seems reasonable or not?
>
> I also need to know the amount of radiation being transmitted through all
> windows of the lower zone (including the virtual screen window) to
> determine the radiation level just above the plants. Does anyone know the
> proper NType for this?
>
> All help is higly appreciated.
>
>
> Kind regards
> Knut Erik Enerstvedt
>
>
>
>
>
>
----------------------------------------------------------------------------------------------------------------------
> NIVAs hovedkontor har flyttet til nye lokaler i CIENS - Forskningssenter
> for miljø og samfunn; Gaustadalléen 21, 0349 Oslo. Meld deg på vårt
> nyhetsbrev på www.niva.no
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
>
>
>
>
--
***********************************************************************
Thermal Energy System Specialists (TESS), LLC
David BRADLEY 22 N. Carroll Street - Suite 370
Partner Madison, WI 53703
USA
P: +1.608.274.2577
F: +1.608.278.1475
E-mail: bradley at tess-inc.com
Web Pages: http://www.tess-inc.com and http://www.trnsys.com
***********************************************************************
----------------------------------------------------------------------------------------------------------------------
NIVAs hovedkontor har flyttet til nye lokaler i CIENS - Forskningssenter
for miljø og samfunn; Gaustadalléen 21, 0349 Oslo. Meld deg på vårt
nyhetsbrev på www.niva.no
More information about the TRNSYS-users
mailing list