Hello,
I'm having a convergence error that seems to be rooted in the PID
controller. I was wondering if anyone could shed some light on the subject.
I'm trying to model a long-haul truck sleeper cabin climate control system.
I'm using a Type 23 PID controller in conjunction with a "seasonal switch"
as the climate control unit. The purpose of the seasonal switch is to turn
the heater on and the air conditioner off when the temperature drops below
some low deadband temperature and vice versa when the temperature rises
above the high deadband temperature. In other words, the purpose of this
switch is to keep the air conditioner from coming on during slight
over-heating and the heater from coming on during slight over-cooling. The
deadband in the seasonal switch is set by default to 5 degrees Celsius.
When just this group of components is run, the output signal from the PID
controller and seasonal switch match just as they should (climate
controller.tpf). However, when a fuel-fired heater (Type 151, homegrown) is
added, the control signal starts doing some crazy stuff (Climate controller
with heater.tpf). The control signals, which should align nicely, start
diverging considerably. This (I assume) creates the convergence error that
stops the simulation after a little more than an hour with the current
settings.
Is there something inherent in the way I am trying to string together these
components that is making the solver diverge? Is there a better way to go
about it? I'm not looking for a total solution- simply a pointer or two
towards why the program is behaving as it is and what I might do to get back
on track. Please let me know if you need any other files.
Thank you in advance for your time,
Ethan Lust
301.405.8672 (desk)
757.636.8727 (cell)
University of Maryland
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20080505/0391e5ca/attachment-0005.htm>
-------------- next part --------------
SUBROUTINE TYPE151 (TIME,XIN,OUT,T,DTDT,PAR,INFO,ICNTRL,*)
C************************************************************************
C Object: Espar D2/D4 direct-fired space heater
C Simulation Studio Model: Type151
C
C Author: Ethan Lust
C Editor:
C Date: March 31, 2008 last modified: April 1, 2008
C
C
C ***
C *** Model Parameters
C ***
C model - [2;4]
C system_voltage V [0;+Inf]
C ***
C *** Model Inputs
C ***
C control_input - [0;+Inf]
C ***
C *** Model Outputs
C ***
C heat_output kJ/hr [0;+Inf]
C fuel_consumption l/hr [0;+Inf]
C air_flow_rate m^3/s [0;+Inf]
C power_draw
C ***
C *** Model Derivatives
C ***
C (Comments and routine interface generated by TRNSYS Studio)
C************************************************************************
C TRNSYS acess functions (allow to acess TIME etc.)
USE TrnsysConstants
USE TrnsysFunctions
C-----------------------------------------------------------------------------------------------------------------------
C REQUIRED BY THE MULTI-DLL VERSION OF TRNSYS
!DEC$ATTRIBUTES DLLEXPORT :: TYPE151 !SET THE CORRECT TYPE NUMBER HERE
C-----------------------------------------------------------------------------------------------------------------------
C-----------------------------------------------------------------------------------------------------------------------
C TRNSYS DECLARATIONS
IMPLICIT NONE !REQUIRES THE USER TO DEFINE ALL VARIABLES BEFORE USING THEM
DOUBLE PRECISION XIN !THE ARRAY FROM WHICH THE INPUTS TO THIS TYPE WILL BE RETRIEVED
DOUBLE PRECISION OUT !THE ARRAY WHICH WILL BE USED TO STORE THE OUTPUTS FROM THIS TYPE
DOUBLE PRECISION TIME !THE CURRENT SIMULATION TIME - YOU MAY USE THIS VARIABLE BUT DO NOT SET IT!
DOUBLE PRECISION PAR !THE ARRAY FROM WHICH THE PARAMETERS FOR THIS TYPE WILL BE RETRIEVED
DOUBLE PRECISION STORED !THE STORAGE ARRAY FOR HOLDING VARIABLES FROM TIMESTEP TO TIMESTEP
DOUBLE PRECISION T !AN ARRAY CONTAINING THE RESULTS FROM THE DIFFERENTIAL EQUATION SOLVER
DOUBLE PRECISION DTDT !AN ARRAY CONTAINING THE DERIVATIVES TO BE PASSED TO THE DIFF.EQ. SOLVER
INTEGER*4 INFO(15) !THE INFO ARRAY STORES AND PASSES VALUABLE INFORMATION TO AND FROM THIS TYPE
INTEGER*4 NP,NI,NOUT,ND !VARIABLES FOR THE MAXIMUM NUMBER OF PARAMETERS,INPUTS,OUTPUTS AND DERIVATIVES
INTEGER*4 NPAR,NIN,NDER !VARIABLES FOR THE CORRECT NUMBER OF PARAMETERS,INPUTS,OUTPUTS AND DERIVATIVES
INTEGER*4 IUNIT,ITYPE !THE UNIT NUMBER AND TYPE NUMBER FOR THIS COMPONENT
INTEGER*4 ICNTRL !AN ARRAY FOR HOLDING VALUES OF CONTROL FUNCTIONS WITH THE NEW SOLVER
INTEGER*4 NSTORED !THE NUMBER OF VARIABLES THAT WILL BE PASSED INTO AND OUT OF STORAGE
CHARACTER*3 OCHECK !AN ARRAY TO BE FILLED WITH THE CORRECT VARIABLE TYPES FOR THE OUTPUTS
CHARACTER*3 YCHECK !AN ARRAY TO BE FILLED WITH THE CORRECT VARIABLE TYPES FOR THE INPUTS
C-----------------------------------------------------------------------------------------------------------------------
C-----------------------------------------------------------------------------------------------------------------------
C USER DECLARATIONS - SET THE MAXIMUM NUMBER OF PARAMETERS (NP), INPUTS (NI),
C OUTPUTS (NOUT), AND DERIVATIVES (ND) THAT MAY BE SUPPLIED FOR THIS TYPE
PARAMETER (NP=2,NI=1,NOUT=4,ND=0,NSTORED=0)
C-----------------------------------------------------------------------------------------------------------------------
C-----------------------------------------------------------------------------------------------------------------------
C REQUIRED TRNSYS DIMENSIONS
DIMENSION XIN(NI),OUT(NOUT),PAR(NP),YCHECK(NI),OCHECK(NOUT),
1 STORED(NSTORED),T(ND),DTDT(ND)
INTEGER NITEMS
C-----------------------------------------------------------------------------------------------------------------------
C-----------------------------------------------------------------------------------------------------------------------
C ADD DECLARATIONS AND DEFINITIONS FOR THE USER-VARIABLES HERE
C PARAMETERS
INTEGER model
INTEGER system_voltage
C INPUTS
DOUBLE PRECISION control_input
C OUTPUTS
DOUBLE PRECISION heat_output
DOUBLE PRECISION fuel_consumption
DOUBLE PRECISION air_flow_rate
DOUBLE PRECISION power_draw
C-----------------------------------------------------------------------------------------------------------------------
C READ IN THE VALUES OF THE PARAMETERS IN SEQUENTIAL ORDER
model=PAR(1)
system_voltage=PAR(2)
C-----------------------------------------------------------------------------------------------------------------------
C RETRIEVE THE CURRENT VALUES OF THE INPUTS TO THIS MODEL FROM THE XIN ARRAY IN SEQUENTIAL ORDER
control_input=XIN(1)
IUNIT=INFO(1)
ITYPE=INFO(2)
C-----------------------------------------------------------------------------------------------------------------------
C SET THE VERSION INFORMATION FOR TRNSYS
IF(INFO(7).EQ.-2) THEN
INFO(12)=16
RETURN 1
ENDIF
C-----------------------------------------------------------------------------------------------------------------------
C-----------------------------------------------------------------------------------------------------------------------
C DO ALL THE VERY LAST CALL OF THE SIMULATION MANIPULATIONS HERE
IF (INFO(8).EQ.-1) THEN
RETURN 1
ENDIF
C-----------------------------------------------------------------------------------------------------------------------
C-----------------------------------------------------------------------------------------------------------------------
C PERFORM ANY 'AFTER-ITERATION' MANIPULATIONS THAT ARE REQUIRED HERE
C e.g. save variables to storage array for the next timestep
IF (INFO(13).GT.0) THEN
NITEMS=0
C STORED(1)=... (if NITEMS > 0)
C CALL setStorageVars(STORED,NITEMS,INFO)
RETURN 1
ENDIF
C
C-----------------------------------------------------------------------------------------------------------------------
C-----------------------------------------------------------------------------------------------------------------------
C DO ALL THE VERY FIRST CALL OF THE SIMULATION MANIPULATIONS HERE
IF (INFO(7).EQ.-1) THEN
C SET SOME INFO ARRAY VARIABLES TO TELL THE TRNSYS ENGINE HOW THIS TYPE IS TO WORK
INFO(6)=NOUT
INFO(9)=1
INFO(10)=0 !STORAGE FOR VERSION 16 HAS BEEN CHANGED
C SET THE REQUIRED NUMBER OF INPUTS, PARAMETERS AND DERIVATIVES THAT THE USER SHOULD SUPPLY IN THE INPUT FILE
C IN SOME CASES, THE NUMBER OF VARIABLES MAY DEPEND ON THE VALUE OF PARAMETERS TO THIS MODEL....
NIN=NI
NPAR=NP
NDER=ND
C CALL THE TYPE CHECK SUBROUTINE TO COMPARE WHAT THIS COMPONENT REQUIRES TO WHAT IS SUPPLIED IN
C THE TRNSYS INPUT FILE
CALL TYPECK(1,INFO,NIN,NPAR,NDER)
C SET THE NUMBER OF STORAGE SPOTS NEEDED FOR THIS COMPONENT
NITEMS=0
C CALL setStorageSize(NITEMS,INFO)
C RETURN TO THE CALLING PROGRAM
RETURN 1
ENDIF
C-----------------------------------------------------------------------------------------------------------------------
C-----------------------------------------------------------------------------------------------------------------------
C DO ALL OF THE INITIAL TIMESTEP MANIPULATIONS HERE - THERE ARE NO ITERATIONS AT THE INTIAL TIME
IF (TIME .LT. (getSimulationStartTime() +
. getSimulationTimeStep()/2.D0)) THEN
C SET THE UNIT NUMBER FOR FUTURE CALLS
IUNIT=INFO(1)
ITYPE=INFO(2)
C CHECK THE PARAMETERS FOR PROBLEMS AND RETURN FROM THE SUBROUTINE IF AN ERROR IS FOUND
C IF(...) CALL TYPECK(-4,INFO,0,"BAD PARAMETER #",0)
C PERFORM ANY REQUIRED CALCULATIONS TO SET THE INITIAL VALUES OF THE OUTPUTS HERE
C heat_output
OUT(1)=0
C fuel_consumption
OUT(2)=0
C air_flow_rate
OUT(3)=0
C power_draw
OUT(4)=0
C PERFORM ANY REQUIRED CALCULATIONS TO SET THE INITIAL STORAGE VARIABLES HERE
NITEMS=0
C STORED(1)=...
C PUT THE STORED ARRAY IN THE GLOBAL STORED ARRAY
C CALL setStorageVars(STORED,NITEMS,INFO)
C RETURN TO THE CALLING PROGRAM
RETURN 1
ENDIF
C-----------------------------------------------------------------------------------------------------------------------
C-----------------------------------------------------------------------------------------------------------------------
C *** ITS AN ITERATIVE CALL TO THIS COMPONENT ***
C-----------------------------------------------------------------------------------------------------------------------
C-----------------------------------------------------------------------------------------------------------------------
C RETRIEVE THE VALUES IN THE STORAGE ARRAY FOR THIS ITERATION
C NITEMS=
C CALL getStorageVars(STORED,NITEMS,INFO)
C STORED(1)=
C-----------------------------------------------------------------------------------------------------------------------
C-----------------------------------------------------------------------------------------------------------------------
C CHECK THE INPUTS FOR PROBLEMS
C IF(...) CALL TYPECK(-3,INFO,'BAD INPUT #',0,0)
C IF(IERROR.GT.0) RETURN 1
C-----------------------------------------------------------------------------------------------------------------------
C-----------------------------------------------------------------------------------------------------------------------
C *** PERFORM ALL THE CALCULATION HERE FOR THIS MODEL. ***
C-----------------------------------------------------------------------------------------------------------------------
C ADD YOUR COMPONENT EQUATIONS HERE; BASICALLY THE EQUATIONS THAT WILL
C CALCULATE THE OUTPUTS BASED ON THE PARAMETERS AND THE INPUTS. REFER TO
C CHAPTER 3 OF THE TRNSYS VOLUME 1 MANUAL FOR DETAILED INFORMATION ON
C WRITING TRNSYS COMPONENTS.
!Assumptions
!*startup power is negligable over long time scales
!D2 Output calculations
IF (model .EQ. 2) THEN
IF (control_input .GT. 0 .AND. control_input .LE. .25) THEN !low
heat_output = 3060 !(kJ/hr)
IF (system_voltage .EQ. 12) THEN
power_draw = system_voltage*0.7*3.6 !(kJ/hr)
ELSE IF (system_voltage .EQ. 24) THEN
power_draw = system_voltage*0.3*3.6 !(kJ/hr)
END IF
fuel_consumption = 0.10 !(L/hr)
air_flow_rate = 0.008968 !(m^3/s)
ELSE IF (control_input .GT.0.25 .AND. control_input .LE. 0.5) THEN !medium
heat_output = 4320 !(kJ/hr)
IF (system_voltage .EQ. 12) THEN
power_draw = system_voltage*1.0*3.6 !(kJ/hr)
ELSE IF (system_voltage .EQ. 24) THEN
power_draw = system_voltage*0.5*3.6 !(kJ/hr)
END IF
fuel_consumption = 0.14 !(L/hr)
air_flow_rate = 0.012744 !(m^3/s)
ELSE IF (control_input .GT. 0.5 .AND. control_input .LE. 0.75) THEN !high
heat_output = 6480 !(kJ/hr)
IF (system_voltage .EQ. 12) THEN
power_draw = system_voltage*1.9*3.6 !(kJ/hr)
ELSE IF (system_voltage .EQ. 24) THEN
power_draw = system_voltage*1.0*3.6 !(kJ/hr)
END IF
fuel_consumption = 0.23 !(L/hr)
air_flow_rate = 0.01888 !(m^3/s)
ELSE IF (control_input .GT. 0.75 .AND. control_input .LE. 1) THEN !boost
heat_output = 7920 !(kJ/hr)
IF (system_voltage .EQ. 12) THEN
power_draw = system_voltage*1.4*3.6 !(kJ/hr)
ELSE IF (system_voltage .EQ. 24) THEN
power_draw = system_voltage*2.8*3.6 !(kJ/hr)
END IF
fuel_consumption = 0.28 !(L/hr)
air_flow_rate = 0.022656 !(m^3/s)
ELSE !off
heat_output = 0 !(kJ/hr)
power_draw = 0 !(kJ/hr)
fuel_consumption = 0 !(L/hr)
air_flow_rate = 0 !(m^3/s)
END IF
END IF
!D4 Output calculations
IF (model .EQ. 4) THEN
IF (control_input .GT. 0 .AND. control_input .LE. .25) THEN !low
heat_output = 3600 !(kJ/hr)
IF (system_voltage .EQ. 12) THEN
power_draw = system_voltage*0.6*3.6 !(kJ/hr)
ELSE IF (system_voltage .EQ. 24) THEN
power_draw = system_voltage*0.3*3.6 !(kJ/hr)
END IF
fuel_consumption = 0.13 !(L/hr)
air_flow_rate = 0.01416 !(m^3/s)
ELSE IF (control_input .GT. .25 .AND. control_input .LE. 0.5) THEN !medium
heat_output = 7200 !(kJ/hr)
IF (system_voltage .EQ. 12) THEN
power_draw = system_voltage*1.1*3.6 !(kJ/hr)
ELSE IF (system_voltage .EQ. 24) THEN
power_draw = system_voltage*0.5*3.6 !(kJ/hr)
END IF
fuel_consumption = 0.25 !(L/hr)
air_flow_rate = 0.0236 !(m^3/s)
ELSE IF (control_input .GT. 0.5 .AND. control_input .LE. 0.75) THEN !high
heat_output = 10800 !(kJ/hr)
IF (system_voltage .EQ. 12) THEN
power_draw = system_voltage*2.0*3.6 !(kJ/hr)
ELSE IF (system_voltage .EQ. 24) THEN
power_draw = system_voltage*1.0*3.6 !(kJ/hr)
END IF
fuel_consumption = 0.38 !(L/hr)
air_flow_rate = 0.032568 !(m^3/s)
ELSE IF (control_input .GT. 0.75 .AND. control_input .LE. 1) THEN !boost
heat_output = 14400 !(kJ/hr)
IF (system_voltage .EQ. 12) THEN
power_draw = system_voltage*3.3*3.6 !(kJ/hr)
ELSE IF (system_voltage .EQ. 24) THEN
power_draw = system_voltage*1.7*3.6 !(kJ/hr)
END IF
fuel_consumption = 0.51 !(L/hr)
air_flow_rate = 0.04012 !(m^3/s)
ELSE !off
heat_output = 0 !(kJ/hr)
power_draw = 0 !(kJ/hr)
fuel_consumption = 0 !(L/hr)
air_flow_rate = 0 !(m^3/s)
END IF
END IF
C-----------------------------------------------------------------------------------------------------------------------
C-----------------------------------------------------------------------------------------------------------------------
C-----------------------------------------------------------------------------------------------------------------------
C SET THE STORAGE ARRAY AT THE END OF THIS ITERATION IF NECESSARY
C NITEMS=
C STORED(1)=
C CALL setStorageVars(STORED,NITEMS,INFO)
C-----------------------------------------------------------------------------------------------------------------------
C-----------------------------------------------------------------------------------------------------------------------
C REPORT ANY PROBLEMS THAT HAVE BEEN FOUND USING CALLS LIKE THIS:
C CALL MESSAGES(-1,'put your message here','MESSAGE',IUNIT,ITYPE)
C CALL MESSAGES(-1,'put your message here','WARNING',IUNIT,ITYPE)
C CALL MESSAGES(-1,'put your message here','SEVERE',IUNIT,ITYPE)
C CALL MESSAGES(-1,'put your message here','FATAL',IUNIT,ITYPE)
C-----------------------------------------------------------------------------------------------------------------------
C-----------------------------------------------------------------------------------------------------------------------
C SET THE OUTPUTS FROM THIS MODEL IN SEQUENTIAL ORDER AND GET OUT
C heat_output
OUT(1)=heat_output
C fuel_consumption
OUT(2)=fuel_consumption
C air_flow_rate
OUT(3)=air_flow_rate
C power_draw
OUT(4)=power_draw
C-----------------------------------------------------------------------------------------------------------------------
C EVERYTHING IS DONE - RETURN FROM THIS SUBROUTINE AND MOVE ON
RETURN 1
END
C-----------------------------------------------------------------------------------------------------------------------
-------------- next part --------------
SUBROUTINE TYPE200 (TIME,XIN,OUT,T,DTDT,PAR,INFO,ICNTRL,*)
!************************************************************************
! Object: Seasonal Switch
! Simulation Studio Model: Type200
!
! Author: Ethan Lust
! Editor:
! Date: April 23, 2008 last modified: April 23, 2008
!
!
! ***
! *** Model Parameters
! ***
! setpoint C [-Inf;+Inf]
! deadband C [0;+Inf]
! ***
! *** Model Inputs
! ***
! input_signal - [-Inf;+Inf]
! T_space ! [-Inf;+Inf]
! ***
! *** Model Outputs
! ***
! output_signal - [-Inf;+Inf]
! switch - [0;1]
! ***
! *** Model Derivatives
! ***
! (Comments and routine interface generated by TRNSYS Studio)
!************************************************************************
! TRNSYS acess functions (allow to acess TIME etc.)
USE TrnsysConstants
USE TrnsysFunctions
!-----------------------------------------------------------------------------------------------------------------------
! REQUIRED BY THE MULTI-DLL VERSION OF TRNSYS
!DEC$ATTRIBUTES DLLEXPORT :: TYPE200 !SET THE CORRECT TYPE NUMBER HERE
!-----------------------------------------------------------------------------------------------------------------------
!-----------------------------------------------------------------------------------------------------------------------
! TRNSYS DECLARATIONS
IMPLICIT NONE !REQUIRES THE USER TO DEFINE ALL VARIABLES BEFORE USING THEM
DOUBLE PRECISION XIN !THE ARRAY FROM WHICH THE INPUTS TO THIS TYPE WILL BE RETRIEVED
DOUBLE PRECISION OUT !THE ARRAY WHICH WILL BE USED TO STORE THE OUTPUTS FROM THIS TYPE
DOUBLE PRECISION TIME !THE CURRENT SIMULATION TIME - YOU MAY USE THIS VARIABLE BUT DO NOT SET IT!
DOUBLE PRECISION PAR !THE ARRAY FROM WHICH THE PARAMETERS FOR THIS TYPE WILL BE RETRIEVED
DOUBLE PRECISION STORED !THE STORAGE ARRAY FOR HOLDING VARIABLES FROM TIMESTEP TO TIMESTEP
DOUBLE PRECISION T !AN ARRAY CONTAINING THE RESULTS FROM THE DIFFERENTIAL EQUATION SOLVER
DOUBLE PRECISION DTDT !AN ARRAY CONTAINING THE DERIVATIVES TO BE PASSED TO THE DIFF.EQ. SOLVER
INTEGER*4 INFO(15) !THE INFO ARRAY STORES AND PASSES VALUABLE INFORMATION TO AND FROM THIS TYPE
INTEGER*4 NP,NI,NOUT,ND !VARIABLES FOR THE MAXIMUM NUMBER OF PARAMETERS,INPUTS,OUTPUTS AND DERIVATIVES
INTEGER*4 NPAR,NIN,NDER !VARIABLES FOR THE CORRECT NUMBER OF PARAMETERS,INPUTS,OUTPUTS AND DERIVATIVES
INTEGER*4 IUNIT,ITYPE !THE UNIT NUMBER AND TYPE NUMBER FOR THIS COMPONENT
INTEGER*4 ICNTRL !AN ARRAY FOR HOLDING VALUES OF CONTROL FUNCTIONS WITH THE NEW SOLVER
INTEGER*4 NSTORED !THE NUMBER OF VARIABLES THAT WILL BE PASSED INTO AND OUT OF STORAGE
CHARACTER*3 OCHECK !AN ARRAY TO BE FILLED WITH THE CORRECT VARIABLE TYPES FOR THE OUTPUTS
CHARACTER*3 YCHECK !AN ARRAY TO BE FILLED WITH THE CORRECT VARIABLE TYPES FOR THE INPUTS
!-----------------------------------------------------------------------------------------------------------------------
!-----------------------------------------------------------------------------------------------------------------------
! USER DECLARATIONS - SET THE MAXIMUM NUMBER OF PARAMETERS (NP), INPUTS (NI),
! OUTPUTS (NOUT), AND DERIVATIVES (ND) THAT MAY BE SUPPLIED FOR THIS TYPE
PARAMETER (NP=2,NI=3,NOUT=2,ND=0,NSTORED=1)
!-----------------------------------------------------------------------------------------------------------------------
!-----------------------------------------------------------------------------------------------------------------------
! REQUIRED TRNSYS DIMENSIONS
DIMENSION XIN(NI),OUT(NOUT),PAR(NP),YCHECK(NI),OCHECK(NOUT),
1 STORED(NSTORED),T(ND),DTDT(ND)
INTEGER NITEMS
!-----------------------------------------------------------------------------------------------------------------------
!-----------------------------------------------------------------------------------------------------------------------
! ADD DECLARATIONS AND DEFINITIONS FOR THE USER-VARIABLES HERE
! PARAMETERS
DOUBLE PRECISION setpoint
DOUBLE PRECISION deadband
! INPUTS
DOUBLE PRECISION input_signal
DOUBLE PRECISION T_space
! OUTPUTS
DOUBLE PRECISION output_signal
DOUBLE PRECISION switch
! LOCAL VARIABLE
DOUBLE PRECISION error
!-----------------------------------------------------------------------------------------------------------------------
! READ IN THE VALUES OF THE PARAMETERS IN SEQUENTIAL ORDER
setpoint=PAR(1)
deadband=PAR(2)
!-----------------------------------------------------------------------------------------------------------------------
! RETRIEVE THE CURRENT VALUES OF THE INPUTS TO THIS MODEL FROM THE XIN ARRAY IN SEQUENTIAL ORDER
input_signal=XIN(1)
T_space = XIN(2)
switch = XIN(3)
IUNIT=INFO(1)
ITYPE=INFO(2)
!-----------------------------------------------------------------------------------------------------------------------
! SET THE VERSION INFORMATION FOR TRNSYS
IF(INFO(7).EQ.-2) THEN
INFO(12)=16
RETURN 1
ENDIF
!-----------------------------------------------------------------------------------------------------------------------
!-----------------------------------------------------------------------------------------------------------------------
! DO ALL THE VERY LAST CALL OF THE SIMULATION MANIPULATIONS HERE
IF (INFO(8).EQ.-1) THEN
RETURN 1
ENDIF
!-----------------------------------------------------------------------------------------------------------------------
!-----------------------------------------------------------------------------------------------------------------------
! PERFORM ANY 'AFTER-ITERATION' MANIPULATIONS THAT ARE REQUIRED HERE
! e.g. save variables to storage array for the next timestep
! IF (INFO(13).GT.0) THEN
! NITEMS=1
! STORED(1)= switch
! CALL setStorageVars(STORED,NITEMS,INFO)
! RETURN 1
! ENDIF
!
!-----------------------------------------------------------------------------------------------------------------------
!-----------------------------------------------------------------------------------------------------------------------
! DO ALL THE VERY FIRST CALL OF THE SIMULATION MANIPULATIONS HERE
IF (INFO(7).EQ.-1) THEN
! SET SOME INFO ARRAY VARIABLES TO TELL THE TRNSYS ENGINE HOW THIS TYPE IS TO WORK
INFO(6)=NOUT
INFO(9)=1
INFO(10)=0 !STORAGE FOR VERSION 16 HAS BEEN CHANGED
! SET THE REQUIRED NUMBER OF INPUTS, PARAMETERS AND DERIVATIVES THAT THE USER SHOULD SUPPLY IN THE INPUT FILE
! IN SOME CASES, THE NUMBER OF VARIABLES MAY DEPEND ON THE VALUE OF PARAMETERS TO THIS MODEL....
NIN=NI
NPAR=NP
NDER=ND
! CALL THE TYPE CHECK SUBROUTINE TO COMPARE WHAT THIS COMPONENT REQUIRES TO WHAT IS SUPPLIED IN
! THE TRNSYS INPUT FILE
CALL TYPECK(1,INFO,NIN,NPAR,NDER)
! SET THE NUMBER OF STORAGE SPOTS NEEDED FOR THIS COMPONENT
! NITEMS=1
! CALL setStorageSize(NITEMS,INFO)
! RETURN TO THE CALLING PROGRAM
RETURN 1
ENDIF
!-----------------------------------------------------------------------------------------------------------------------
!-----------------------------------------------------------------------------------------------------------------------
! DO ALL OF THE INITIAL TIMESTEP MANIPULATIONS HERE - THERE ARE NO ITERATIONS AT THE INTIAL TIME
IF (TIME .LT. (getSimulationStartTime() +
. getSimulationTimeStep()/2.D0)) THEN
! SET THE UNIT NUMBER FOR FUTURE CALLS
IUNIT=INFO(1)
ITYPE=INFO(2)
! CHECK THE PARAMETERS FOR PROBLEMS AND RETURN FROM THE SUBROUTINE IF AN ERROR IS FOUND
! IF(...) CALL TYPECK(-4,INFO,0,"BAD PARAMETER #",0)
! PERFORM ANY REQUIRED CALCULATIONS TO SET THE INITIAL VALUES OF THE OUTPUTS HERE
! output_signal
OUT(1)=0
! switch
! OUT(2)=0
! PERFORM ANY REQUIRED CALCULATIONS TO SET THE INITIAL STORAGE VARIABLES HERE
! NITEMS=1
! STORED(1)= 0
! PUT THE STORED ARRAY IN THE GLOBAL STORED ARRAY
! CALL setStorageVars(STORED,NITEMS,INFO)
! RETURN TO THE CALLING PROGRAM
RETURN 1
ENDIF
!-----------------------------------------------------------------------------------------------------------------------
!-----------------------------------------------------------------------------------------------------------------------
! *** ITS AN ITERATIVE CALL TO THIS COMPONENT ***
!-----------------------------------------------------------------------------------------------------------------------
!-----------------------------------------------------------------------------------------------------------------------
! RETRIEVE THE VALUES IN THE STORAGE ARRAY FOR THIS ITERATION
! NITEMS= 1
! CALL getStorageVars(STORED,NITEMS,INFO)
! STORED(1)= switch
!-----------------------------------------------------------------------------------------------------------------------
!-----------------------------------------------------------------------------------------------------------------------
! CHECK THE INPUTS FOR PROBLEMS
! IF(...) CALL TYPECK(-3,INFO,'BAD INPUT #',0,0)
! IF(IERROR.GT.0) RETURN 1
!-----------------------------------------------------------------------------------------------------------------------
!-----------------------------------------------------------------------------------------------------------------------
! *** PERFORM ALL THE CALCULATION HERE FOR THIS MODEL. ***
!-----------------------------------------------------------------------------------------------------------------------
input_signal = abs(input_signal)
error = setpoint - T_space
if (switch .EQ. 0D0) then
if (error .LE. -deadband) then
switch = 1D0 !Turns A/C on and heat off
end if
else if (switch .EQ. 1D0) then
if (error .GE. deadband) then
switch = 0D0 !Turns heat on and A/C off
end if
end if
if (switch .EQ. 0D0) then
if (error .GE. 0) then
output_signal = input_signal
else if (error .LT. 0) then
output_signal = 0
end if
else if (switch .EQ. 1D0) then
if (error .LE. 0) then
output_signal = -input_signal
else if (error .GT. 0) then
output_signal = 0
end if
end if
!-----------------------------------------------------------------------------------------------------------------------
!-----------------------------------------------------------------------------------------------------------------------
!-----------------------------------------------------------------------------------------------------------------------
! SET THE STORAGE ARRAY AT THE END OF THIS ITERATION IF NECESSARY
! NITEMS= 1
! STORED(1)= switch
! CALL setStorageVars(STORED,NITEMS,INFO)
!-----------------------------------------------------------------------------------------------------------------------
!-----------------------------------------------------------------------------------------------------------------------
! REPORT ANY PROBLEMS THAT HAVE BEEN FOUND USING CALLS LIKE THIS:
! CALL MESSAGES(-1,'put your message here','MESSAGE',IUNIT,ITYPE)
! CALL MESSAGES(-1,'put your message here','WARNING',IUNIT,ITYPE)
! CALL MESSAGES(-1,'put your message here','SEVERE',IUNIT,ITYPE)
! CALL MESSAGES(-1,'put your message here','FATAL',IUNIT,ITYPE)
!-----------------------------------------------------------------------------------------------------------------------
!-----------------------------------------------------------------------------------------------------------------------
! SET THE OUTPUTS FROM THIS MODEL IN SEQUENTIAL ORDER AND GET OUT
! output_signal
OUT(1) = output_signal
! switch
OUT(2) = switch
!-----------------------------------------------------------------------------------------------------------------------
! EVERYTHING IS DONE - RETURN FROM THIS SUBROUTINE AND MOVE ON
RETURN 1
END
!-----------------------------------------------------------------------------------------------------------------------
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Type151.tmf
Type: application/octet-stream
Size: 895 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20080505/0391e5ca/attachment-0020.obj>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Type200.tmf
Type: application/octet-stream
Size: 848 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20080505/0391e5ca/attachment-0021.obj>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Climate Controller.tpf
Type: application/octet-stream
Size: 87432 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20080505/0391e5ca/attachment-0022.obj>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Climate Controller with heater.tpf
Type: application/octet-stream
Size: 139170 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20080505/0391e5ca/attachment-0023.obj>
More information about the TRNSYS-users
mailing list