[TRNSYS-users] FW: Pond component
David Bradley
bradley at tess-inc.com
Wed Mar 19 06:49:07 PDT 2008
Kent,
I think that the DLL you are running and the Fortran code that you
attached are not quite the same. I had to make a few changes in the
source code before I was able to run the project that you sent. When I
did run the project, I got an error when the variable PRPIPEFILM got set
to a negative number, then got raised to a non integer power during the
Type's iteration. The offending equation is:
NUPIPEFILM=(0.6+0.387*RAPIPEFILM**(1./6.)/(1+(0.559/PRPIPEFILM)**(9./16.))**(8./27.))**2.
I hope that helps...
David
Kent Beason wrote:
>
> I am having trouble with a pond component, Type 230. I keep getting
> an error regarding the psychrometrics subroutine, that the subroutine
> has been called with a wet bulb temp above the max wet bulb temp for
> the given pressure right after the sim starts. Any suggestions on
> where the problem may be?
>
>
>
> ------------------------------------------------------------------------
>
> *From:* Kent Beason
> *Sent:* Monday, February 25, 2008 5:21 PM
> *To:* David Bradley
> *Subject:* Pond component
>
>
>
> David,
>
>
>
> Attached are the studio file, list file, and source code file of the
> pond component. The "replace" command which we last discussed did
> eliminate the 2 errors at that time, but now there is 1 error
> regarding the Psychrometrics utility routine and the simulation
> crashes at .13hour.
>
>
>
> Thanks for taking a look at this, and see you tomorrow.
>
>
>
> Kent
>
--
***********************************************************************
Thermal Energy System Specialists (TESS), LLC
David BRADLEY 2916 Marketplace Drive - Suite 104
Partner Madison, WI 53719
USA
P: +1.608.274.2577
F: +1.608.278.1475
E-mail: bradley at tess-inc.com
Web Pages: http://www.tess-inc.com and http://www.trnsys.com
***********************************************************************
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20080319/76046e48/attachment-0005.htm>
More information about the TRNSYS-users
mailing list