[TRNSYS-users] problem with type 109 user format

Eleni Ampatzi ampatzie at Cardiff.ac.uk
Mon Mar 3 11:32:55 PST 2008


Dear Stefan,

Thank you for your answer. But I did not understand what you suggest. The measurements I use are in
local time, which is GMT. I should not have this problem then, isn't it?

Eleni

>>> "Wolf, Stefan" <Stefan.Wolf at muellerbbm.de> 03/03/08 6:33 PM >>>
I didn't check your files, but maybe this help you:
solar radiation is often measured in solar time, not in local time.
if you treat solar time measurements as local time data, the position of sun
doesn't fit to the measurements (example: values >0 W/m2at times when the
sun is down).  
-> use param. 9 in TYPE 16.

Stefan

> -----Original Message-----
> From: Eleni Ampatzi [mailto:ampatzie at Cardiff.ac.uk]
> Sent: Monday, March 03, 2008 5:04 PM
> To: trnsys-users at engr.wisc.edu
> Subject: [TRNSYS-users] problem with type 109 user format
> 
> 
> Dear All,
> 
> I am using type 109 in mode 1 to read my weather data for 
> Cardiff. The data I am using is in 5 min
> intervals (from local weather station, measurements for year 
> 2007). The problem is that I get
> warnings in the List file saying that the data includes 
> isnolation values >0 W/m2at times when the
> sun is down (and then the software sets this values to 0). I 
> cannot find the mistake in my *.109.
> Can someone take a look in the attached file and help me? It 
> will be much appreciated...
> 
> Best Regards
> 
> Eleni Ampatzi
> PhD Student, WSA, Cardiff University
> 
_______________________________________________
TRNSYS-users mailing list
TRNSYS-users at engr.wisc.edu
https://www.cae.wisc.edu/mailman/listinfo/trnsys-users




More information about the TRNSYS-users mailing list