[TRNSYS-users] Convergence problems with type 56 possibly involving cooling load
David Bradley
bradley at tess-inc.com
Thu Jun 19 12:22:07 PDT 2008
Ethan,
There are two ways of conditioning a Type56 thermal zone: energy rate
control and temperature level control and I think that what is happening
in your simulation is that the two are getting mixed. When you work in
energy rate control, you define the temperature of the zone and you
calculate the amount of energy that is required to meet that set point.
Because you predefined the set point, you are in essence assuming that
your HVAC system is able to meet that set point. When you work in
temperature level control, the zone becomes just another component in
the system; its temperature and humidity are a result of both ambient
and the systems that try to keep them at set point. In your simulation,
you have defined a set point and then are modulating the capacity of the
cooling system at the same time. I think what you want to do is one of
the following:
Define the set point and allow the capacity to be unlimited and
calculate the cooling loads, then afterwards, impose those loads on your
CCU and make sure that it can meet them at all times.
or
Define a thermostat model (Type23 perhaps) that monitors the cabin
temperature and Type56 ventilation inputs (T, RH, and ach). Have the
thermostat command your CCU and pass its outlet temperature, flow rate,
and RH to the Type56 model. The temperature in the cabin will oscillate
around the set point a bit (as it would in reality) as it turns fans up
and down.
I hope that helps,
David
Ethan Lust wrote:
> Hello,
>
> I am trying to simulate the operation of a climate control unit (vapor
> compression air conditioner and electric resistance heater) in a small
> closed space. The climate control unit (CCU) (Type 202 and the accompanying
> DLL7) is an original component created from manufacturer's data. Prior to
> the heater and air conditioning code within the Type202.f code, there is a
> switch that keeps the air conditioner and heater from operating
> simultaneously. The climate control unit is operated via a PID controller
> (Type 23). In addition, the space also has an internal heat load due to
> some electronics, hence the three type 9a components and the Type 41c.
>
> If the heat from the CCU is input into Type 56 through the heating function
> in TRNBuild and the cooling output from the CCU is attached likewise, there
> are a number of points over the course of the TMY2 year at which the program
> "bogs down" and stops with the calculations though no error message is
> produced. Occasionally an error message will pop up stating that there are
> 6 errors (no matter how many I have set to allow within the control cards),
> which all relate to temperature divergence at a wall, according to the list
> file. I have tried increasing the convergence tolerance with no luck.
>
> If the cooling portion is removed, the program proceeds fine, with or
> without the internal loads attached.
>
> I have sought help for a similar problem, to which I was suggested to
> decrease the cooling output and/or decrease the time interval to aid in
> convergence. I've tried reducing the cooling input to very low values (the
> DLL I'm sending has it cut in half) with no luck. The current time interval
> is a dreadfully slow 5 seconds.
>
> I have also tried connecting the cooling output of the CCU to the Type 56
> using the gain function (using a negative value as input) with the same
> result.
>
> Attached are the project, bui, component (fortran and proforma) files and
> the DLL.
>
> Please help!
>
> Thanks,
> Ethan Lust
> University of Maryland
>
> ------------------------------------------------------------------------
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at engr.wisc.edu
> https://www.cae.wisc.edu/mailman/listinfo/trnsys-users
>
--
***********************************************************************
Thermal Energy System Specialists (TESS), LLC
David BRADLEY 2916 Marketplace Drive - Suite 104
Partner Madison, WI 53719
USA
P: +1.608.274.2577
F: +1.608.278.1475
E-mail: bradley at tess-inc.com
Web Pages: http://www.tess-inc.com and http://www.trnsys.com
***********************************************************************
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20080619/6a3b9f66/attachment-0005.htm>
More information about the TRNSYS-users
mailing list