[TRNSYS-users] bug: "stability criteria not fullfilled"
    Matt Duffy 
    duffy at tess-inc.com
       
    Thu Jul 31 14:12:11 PDT 2008
    
    
  
Catherine,
You might want to try increasing the timebase in the Outputs window in
TRNBuild.  Please refer to section 6.4.1.14 in the Multizone Building
Manual for more info.  ASHRAE recommends a timebase of 1 hour, but 2-4
hours may be used for heavy construction (Ref. 6.2.10.9).
Best regards,
Matt Duffy
----- Original Message -----
From: "Catherine Massart" <trnsysmassart at gmail.com>
Sent: Thu, July 31, 2008 8:23
Subject:[TRNSYS-users] bug: "stability criteria not fullfilled"
*Dear TRNSYS users*
**
*I want to make simulations on highly insulated buildings.*
*Some of the walls I created bring a bug.*
**
*« Error creating the wall transfer function coefficients :*
*Stability criteria not fullfilled*
*Check layer definition (thickness, ratio of conductivity/density)*
*Please check the INF-file for further information »*
**
*I heard this could be solved by changing the density and capacity of the
layer that causes the problem (here, a ceiling wood structure insulated with
40cm of wood fiber pannels (Steico))*
*But I cannot do this because I want to evaluate the impact of the inertia
on the inside temperatures.*
*I tried by deviding the material in 2 layers: one would have the same
inertia and the other, massless, would bring the thermical resistance. It
doesn't work, stability criteria is still not fullfilled...*
**
*Can someone help me?*
**
*Thanks a lot*
**
*Catherine Massart*
*UCL-Belgium*
----- End of original message -----
    
    