You need to use an equation and a few Type 14 forcing functions.

Unit 1 Type 14 Forcing Function for Seasonal Switchover
Parameters 12
0,1  2160,1  2160,0  6552,0  6552,1  8760,1

Unit 2 Type 14 Forcing Function for Winter Daily Operation
Parameters 12
0,0  7,0  7,200  18,200  18,0  24,0

Unit 3 Type 14 Forcing Function for Summer Daily Operation
Parameters 12
0,200  7,200  7,1000  18,1000  18,200  24,200

Equations 1
Ventilation=[1,1]*[2,1]+(1-[1,1])*[3,1]

Jeff