Jens,
My guess is that you may need to look at the section of Type534
that reserves space in the global output and storage arrays. Space is
reserved in the OUT() array by setting INFO(6) and then calling
TYPECK() at the start of the simulation. Space is reserved in the
global storage array by calling the SetStorageSize() subroutine. The
problems that you describe sounds like what happens when one
component overwrites the outputs of another.
Kind regards,
David
At 06:17 2/12/2008, Jens Apel wrote:
>Dear all,
>
>I'm using the type 534 storage tank of the TESS libraries. I made a
>small change in the code, I set the maximum number of ports to 20.
>Beside other components I use an online plotter with file to see and
>print the tank nodal temperatures. The system runs ok, but if I
>change the double port of the solar circle I get an invalid floating
>point operation error. This happens only if I have the respective
>plotter switched on and the tank energy balance error connected to
>the plotter. As soon as I switch off the plotter or disconnect the
>balance error everything is alright. In the output file of the
>plotter I get normal values for the balance error and at some times
>it is written "NaN". Those are probably the times where I get the error.
>
>This is no problem for me as I don't necessarily need the balance
>error and so I don't need real help from you. I am just curious what
>the reason might be and if anybody of you ended up with the same behavior.
>
>Thanks for any replies
>
>Jens Apel
>Technical University of Berlin
>_______________________________________________
>TRNSYS-users mailing list
>TRNSYS-users at engr.wisc.edu
>https://www.cae.wisc.edu/mailman/listinfo/trnsys-users
****************************************************************************************
Thermal Energy System Specialists (TESS), LLC
David BRADLEY 2916 Marketplace Drive - Suite 104
Partner Madison, WI 53719
Phone: (608) 274-2577 USA
Fax: (608) 278-1475
E-mail: bradley at tess-inc.com
Web Pages: http://www.tess-inc.com and http://www.trnsys.com
"Providing software solutions for today's energy engineering projects"
****************************************************************************************
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20080212/01853986/attachment-0005.htm>
More information about the TRNSYS-users
mailing list