[TRNSYS-users] How to use Window5 to create a window system with the values expected?
David Bradley
bradley at tess-inc.com
Fri Feb 29 08:01:38 PST 2008
Yujun,
This is a pretty common problem unfortunately. At some point you
will have to just do the best you can. One thing that my colleagues
and I have found helps is to get some idea of the construction of the
window (pane thicknesses, location of films, gas gap thicknesses,
frame descriptions, etc.). These can help guide you and get you
pretty close to the published values. I have not had much luck using
Optic5 to generate new windows. Where I have found Optic5 to be
helpful is that it gives access to the IGDB (International Glazing
Data Base); that data base expands quickly and you can often find the
actual manufacturer and window that you are looking for, export it to
Window5 and avoid all the problems of tuning your window to match the
published data.
Kind regards,
David
At 11:46 2/28/2008, Yujun TAO wrote:
>Dear users,
>Do you know how to use Window5 to create a window system with the
>values expected?
>I want to create a window system with three values followings :
>U=2.1 W/m2.K (overall); g (Solar heat gain factor) =0.6; Visible
>Transmission=0.7
>I can just get sometimes the values "closes", but not so close like
>I wish. So help me if you know
>In advance Thank you for your help.
>Yujun
>
>
>Ne gardez plus qu'une seule adresse mail !
><http://fr.rd.yahoo.com/mail/mail_taglines/trueswitch/SIG=11gshn0bu/**http%3A%2F%2Fwww.trueswitch.com%2Fyahoo-fr%2F>Copiez
>vos mails vers Yahoo! Mail
>_______________________________________________
>TRNSYS-users mailing list
>TRNSYS-users at engr.wisc.edu
>https://www.cae.wisc.edu/mailman/listinfo/trnsys-users
****************************************************************************************
Thermal Energy System Specialists (TESS), LLC
David BRADLEY 2916 Marketplace Drive - Suite 104
Partner Madison, WI 53719
Phone: (608) 274-2577 USA
Fax: (608) 278-1475
E-mail: bradley at tess-inc.com
Web Pages: http://www.tess-inc.com and http://www.trnsys.com
"Providing software solutions for today's energy engineering projects"
****************************************************************************************
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20080229/7065f9d7/attachment-0001.htm>
More information about the TRNSYS-users
mailing list