[TRNSYS-users] radiation

Jeroen Van der Veken Jeroen.VanderVeken at bwk.kuleuven.be
Sun Dec 21 14:14:03 PST 2008


Dear collegues,
I want to model the dynamics of the combination of an hydronic radiator 
and the wall behind it more in detail. To simulate the behaviour of the 
wall behind the radiator, I added an extra zone. This seems to work 
fine, but I ran into another problem.

Usually when modelling a radiator in TRNSYS, the radiation sent out by 
the radiator is regarded as a radiative gain. But regarding comfort, 
this is not correct, since this implies that the radiation is leaving 
from the zone point in the centre and only the part that is reflected by 
the walls is then felt by the person standing in the same zone point. In 
reality a part of the radiation will reach the person directly.

So I built a wall with the same surface and temperature as the radiator 
and a very low convective heat transfer so that only radiation would 
occur and not convection.
This is working fine at the backside of the radiator, but doesn't at the 
front; the average surface temperature and operative temperature of the 
zone seem OK, but the Qcomi of the hot surface is much too high. Qcomi 
only gives a reasonable value (close to the calculated value for 
radiation) when I reduce the size of the other walls in the room.

Is this strange behaviour caused by the star network ? or another 
simplification in TRNSYS? or did I do something wrong ?
I guess I can simply avoid the problem by recalculating the operative 
temperature myself, but I wanted to use the same strategy to model 
stratification of air above the radiator. Or is there another method to 
model stratification; to build an imaginary wall between two zones that 
allows to have two zone temperatures but can still be transparant for 
long wave radiation ?

Is it possible to change the long wave emissivity of inner wall surfaces ?

And is it still possible to change the time base of the transfer 
coefficient calculations ? I seem to remember that I could change it 
manually, but I can't find it anymore...

I guess TRNSYS16 is not the ideal building simulator for this kind of 
intrazonal problems, but all my other heating system models are working 
fine, so it would be nice to stick to it !

Thanks for reading and hopefully answering some of my questions,
best regards,
Jeroen Van der Veken


Disclaimer: http://www.kuleuven.be/cwis/email_disclaimer.htm

-------------- next part --------------
A non-text attachment was scrubbed...
Name: EN442trnsys.tpf
Type: application/octet-stream
Size: 98329 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20081221/2fd68786/attachment-0005.obj>
-------------- next part --------------
*********************************************************************************************************************************************************************************************************
*  TRNBuild   1.0.94
*********************************************************************************************************************************************************************************************************
*   BUILDING DESCRIPTIONS FILE TRNSYS
*   FOR BUILDING:   D:\Jaga\TRNSYS\EN442trnsys.bui
*   GET BY WORKING WITH TRNBuild 1.0 for Windows
*********************************************************************************************************************************************************************************************************
*
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  C o m m e n t s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  P r o j e c t
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*+++ PROJECT
*+++ TITLE=UNDEFINED
*+++ DESCRIPTION=UNDEFINED
*+++ CREATED=UNDEFINED
*+++ ADDRESS=UNDEFINED
*+++ CITY=UNDEFINED
*+++ SWITCH=UNDEFINED
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  P r o p e r t i e s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
PROPERTIES
 DENSITY=1.204 : CAPACITY=1.012 : HVAPOR=2454.0 : SIGMA=2.041e-007 : RTEMP=293.15
*--- alpha calculation -------------------
 KFLOORUP=7.2 : EFLOORUP=0.31 : KFLOORDOWN=3.888 : EFLOORDOWN=0.31
 KCEILUP=7.2 : ECEILUP=0.31 : KCEILDOWN=3.888 : ECEILDOWN=0.31
 KVERTICAL=5.76 : EVERTICAL=0.3
*
*++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++
TYPES
*++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++
*
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  L a y e r s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
LAYER GIPSPLEIST
 CONDUCTIVITY=   2.52 : CAPACITY=      1 : DENSITY=   1400
LAYER LEICHTBETO
 CONDUCTIVITY=    3.2 : CAPACITY=      1 : DENSITY=   1500
LAYER STAHL
 CONDUCTIVITY=     54 : CAPACITY=    0.8 : DENSITY=   7800
LAYER YTONG
 CONDUCTIVITY=  0.432 : CAPACITY=   0.84 : DENSITY=    425
LAYER POLYSTYREN
 CONDUCTIVITY=   0.13 : CAPACITY=   1.25 : DENSITY=     25
LAYER SANDST_MUS
 CONDUCTIVITY=   8.28 : CAPACITY=      1 : DENSITY=   2600
LAYER VLOERMAT
 CONDUCTIVITY=  0.133 : CAPACITY=      1 : DENSITY=    100
LAYER PURHOUT
 CONDUCTIVITY=  0.157 : CAPACITY=    1.6 : DENSITY=    100
LAYER BUITENPLEIST
 CONDUCTIVITY=   1.69 : CAPACITY=      1 : DENSITY=   1400
LAYER WANDBAUPL_
 CONDUCTIVITY=   1.26 : CAPACITY=      1 : DENSITY=    750
LAYER POLYURETHA
 CONDUCTIVITY=  0.101 : CAPACITY=   2.09 : DENSITY=     40
LAYER LAYER001
 RESISTANCE=    0.047
LAYER LAYER002
 PSPACING=    0.1 : PDIAMETER=   0.01 : PWALLTHICKNESS=  0.002 : PCONDUCTIVITY=   1.26 : CPFLUID= 4.18
LAYER YTONG_LICHT
 CONDUCTIVITY=  0.432 : CAPACITY=   1.04 : DENSITY=    425
LAYER NICHTSOLEICHTBETO
 CONDUCTIVITY=      8 : CAPACITY=      3 : DENSITY=   1500
LAYER SPRUCE_PIN
 CONDUCTIVITY=      2 : CAPACITY=      5 : DENSITY=    600
LAYER ALUMINIUM
 CONDUCTIVITY=    720 : CAPACITY=   0.86 : DENSITY=   2700
LAYER MINERAL_WO
 CONDUCTIVITY=   0.14 : CAPACITY=    0.9 : DENSITY=     80
LAYER MASSLESS
 RESISTANCE=      100
LAYER COPPER
 CONDUCTIVITY=   1340 : CAPACITY=  0.419 : DENSITY=   8300
LAYER LAYER003
 RESISTANCE=        1
LAYER LAYER004
 RESISTANCE=      0.1
LAYER LAYER005
 RESISTANCE=     0.01
LAYER NOWALL2
 RESISTANCE=    0.001
LAYER LAYER006
 RESISTANCE=        1
LAYER LAYER007
 RESISTANCE=      100
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  I n p u t s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
INPUTS RADIATORCONV TRAD RADFLOW
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  S c h e d u l e s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  W a l l s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
WALL NOWALL
 LAYERS   = NOWALL2 
 THICKNESS= 0       
 ABS-FRONT= 0     : ABS-BACK= 0    
 HFRONT   = 11 : HBACK= 0.0001
WALL EN442
 LAYERS   = STAHL POLYSTYREN 
 THICKNESS= 0.001 0.1        
 ABS-FRONT= 0.6   : ABS-BACK= 0.6  
 HFRONT   = 11 : HBACK= 64
WALL RADIATOR
 LAYERS   = NOWALL2 
 THICKNESS= 0       
 ABS-FRONT= 0.5   : ABS-BACK= 0.5  
 HFRONT   = 0.0015 : HBACK= 0.0001
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  W i n d o w s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
WINDOW NOWALLW
 WINID=10001 : HINSIDE=64 : HOUTSIDE=64 : SLOPE=90 : SPACID=1 : WWID=1 : WHEIG=1 : FFRAME=0.01 : UFRAME=8.17 : ABSFRAME=1 : RISHADE=0 : RESHADE=0 : REFLISHADE=0.5 : REFLOSHADE=0.5 : CCISHADE=0.5
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  D e f a u l t  G a i n s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  O t h e r  G a i n s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
GAIN RADIATOR
 CONVECTIVE=INPUT 1*RADIATORCONV : RADIATIVE=0 : HUMIDITY=0
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  C o m f o r t
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  I n f i l t r a t i o n
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  V e n t i l a t i o n
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  C o o l i n g
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
COOLING COOL001
 ON=20
 POWER=999999999
 HUMIDITY=100
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  H e a t i n g
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  Z o n e s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONES EN442 RADEN442
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  O r i e n t a t i o n s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ORIENTATIONS NORTH SOUTH EAST WEST HORIZONTAL
*
*++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++
BUILDING
*++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++
*
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  Z o n e  EN442  /  A i r n o d e  EN442
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE EN442
AIRNODE EN442
WALL  =NOWALL     : SURF= 27 : AREA=       200 : BOUNDARY=20
WALL  =EN442      : SURF= 28 : AREA=        19 : BOUNDARY=18
WALL  =NOWALL     : SURF= 31 : AREA=       0.1 : ADJACENT=RADEN442 : BACK : COUPL=INPUT 1*RADFLOW
WALL  =RADIATOR   : SURF=  1 : AREA=         1 : BOUNDARY=INPUT 1*TRAD
 REGIME
 COOLING     = COOL001
 CAPACITANCE = 240     : VOLUME= 200     : TINITIAL= 20      : PHINITIAL= 50      : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  Z o n e  RADEN442  /  A i r n o d e  RADEN442
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE RADEN442
AIRNODE RADEN442
WALL  =RADIATOR   : SURF= 29 : AREA=         1 : BOUNDARY=INPUT 1*TRAD
WALL  =NOWALL     : SURF= 30 : AREA=       0.1 : ADJACENT=EN442 : FRONT : COUPL=INPUT 1*RADFLOW
WALL  =EN442      : SURF= 32 : AREA=         1 : BOUNDARY=20
 REGIME
 GAIN        = RADIATOR   : SCALE= 1
 CAPACITANCE = 0.24    : VOLUME= 0.2     : TINITIAL= 20      : PHINITIAL= 50      : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  O u t p u t s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
OUTPUTS
 TRANSFER : TIMEBASE=1.000
 AIRNODES = RADEN442 EN442 
 NTYPES =   1 : TAIR - air temperature of zone
        =   3 : QCSURF - total convection to air from all surfaces within zone (incl. internal shading)
        =   6 : QCOUP - tsensible coupling energy gain of zone
        =  16 : QTCOMO - total convective and longwave rad. gain to outside surf. of zone
        =  14 : QTABSI - total radiation absorbed (and transmitted) at all inside surf. of zone (inc. solar gains, rad. heat and int. rad. gains and wallgains)
        =  23 : TSTAR - star node temperature of zone
        =  24 : TMSURF - weighted mean surface temperature of zone
        =  25 : TOP - operative zone temperature
 AIRNODES = RADEN442 
 NTYPES =  17 : SURF = 29, 30, 32,  : TSI - inside surface temperature
        =  18 : SURF = 29, 30, 32,  : TSO - outside surface temperature
        =  19 : SURF = 29, 32,  : QCOMI - energy from  inside surface incl. conv. to the air and l-wave radiation to other surfaces
        =  21 : SURF = 29, 32,  : QABSI - total radiation absorbed (and transmitted) at all inside surf. of zone (inc. solar gains, radiative heat and int. rad. gains, but not l-wave radiation from ;
 other walls
        =  84 : SURF = 32,  : QRGAB - internal radiative gains absorbed on inside surface of wall or window
        = 904 : BAL_4 - energy balance for all zones
 AIRNODES = EN442 
 NTYPES =  17 : SURF = 27, 28, 31, 1,  : TSI - inside surface temperature
        =  19 : SURF = 27, 28, 31, 1,  : QCOMI - energy from  inside surface incl. conv. to the air and l-wave radiation to other surfaces
*
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  T R N S F L O W Multizone Airflow Network (Model COMIS 3.1)
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*
*++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++
MULTIZONE_AIRFLOW_NETWORK
*++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++
*
CALCFLOWS=0
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  A d d  T R N S F L O W  C o m m a n d s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*
*++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++
POLLUTANTS
*++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++
*
*
*++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++
LINKTYPES
*++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++
*
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  C r a c k s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  F a n s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  S t r a i g h t   D u c t s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  F l o w   C o n t r o l l e r s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  L a r g e    V e r t i c a l   Openings (Windows+Doors)
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  T e s t   D a t a   C o m p o n e n t s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*
*++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++
NODETYPES
*++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++
*
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  E x t e r n a l   N o d e s  (CP VALUES)
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  A u x i l i a r y   N o d e s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  T h e r m a l  Z o n e   N o d e s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  W i n d   v e  l o c i t y   p r o f i l e
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*
*++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++
WIND_VELOPROF
*++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++
*
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  A i r l i n k   N e t w o r k
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*
*++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++
AIRLINK_NETWORK
*++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++
*
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  E n d
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
END

_EXTENSION_WINPOOL_START_
WINDOW 4.1  DOE-2 Data File : Multi Band Calculation
Unit System : SI
Name        : TRNSYS 14.2 WINDOW LIB
Desc        : Keine Glasscheibe = offen
Window ID   : 10001
Tilt        : 90.0
Glazings    : 1
Frame       : 11                       2.270
Spacer      :  1 Class1                2.330  -0.010   0.138
Total Height: 1219.2 mm
Total Width :  914.4 mm
Glass Height: 1079.5 mm
Glass Width :  774.7 mm
Mullion     : None
Gap        Thick   Cond  dCond    Vis   dVis   Dens   dDens     Pr     dPr
1              0       0      0      0      0      0       0      0       0
2              0       0      0      0      0      0       0      0       0
3              0       0      0      0      0      0       0      0       0
4              0       0      0      0      0      0       0      0       0
5              0       0      0      0      0      0       0      0       0
Angle     0    10    20    30    40    50    60    70    80    90 Hemis
Tsol  1.000 1.000 1.000 1.000 1.000 1.000 1.000 1.000 1.000 1.000 0.999
Abs1  0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.001 0.000 0.001
Abs2      0     0     0     0     0     0     0     0     0     0     0
Abs3      0     0     0     0     0     0     0     0     0     0     0
Abs4      0     0     0     0     0     0     0     0     0     0     0
Abs5      0     0     0     0     0     0     0     0     0     0     0
Abs6      0     0     0     0     0     0     0     0     0     0     0
Rfsol 0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.000
Rbsol 0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.000
Tvis  1.000 1.000 1.000 1.000 1.000 1.000 1.000 1.000 1.000 1.000 0.999
Rfvis 0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.000
Rbvis 0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.000
SHGC  1.000 1.000 1.000 1.000 1.000 1.000 1.000 1.000 1.000 0.000 1.000
SC: 1.0
Layer ID#         9052        0        0        0        0        0
Tir              0.000        0        0        0        0        0
Emis F           1.000        0        0        0        0        0
Emis B           1.000        0        0        0        0        0
Thickness(mm)    0.001        0        0        0        0        0
Cond(W/m2-C     ) 999.0        0        0        0        0        0
Spectral File     None     None     None     None     None     None
Overall and Center of Glass Ig U-values (W/m2-C)
Outdoor Temperature                 -17.8 C      15.6 C      26.7 C      37.8 C
Solar      WdSpd  hcout hrout  hin
(W/m2)     (m/s)     (W/m2-C)
0        0.00  12.25  3.42  8.23  5.27 5.27  4.95 4.95  4.94 4.94  5.53 5.53
0        6.71  25.47  3.33  8.29  6.26 6.26  5.73 5.73  5.68 5.68  6.46 6.46
783        0.00  12.25  3.49  8.17  5.25 5.25  4.58 4.58  5.24 5.24  5.66 5.66
783        6.71  25.47  3.37  8.27  6.25 6.25  5.53 5.53  5.95 5.95  6.57 6.57
WINDOW 4.1  DOE-2 Data File : Multi Band Calculation
Unit System : SI
Name        : TRNSYS15 WINDOW LIB
Desc        : Saint Gobain CLIMAPLUS FUTUR AR 1.1  4/15/4
Window ID   : 13002
Tilt        : 90.0
Glazings    : 2
Frame       : 11 TRNSYS WIN - 1        2.270
Spacer      :  1 Class1                2.330  -0.010   0.138
Total Height: 1600.0 mm
Total Width : 1250.0 mm
Glass Height: 1460.3 mm
Glass Width : 1110.3 mm
Mullion     : None
Gap        Thick   Cond  dCond    Vis   dVis   Dens   dDens     Pr     dPr
1 Argon     15.0 0.01620  5.000  2.110  6.300  1.780 -0.0060  0.680 0.00066
2              0       0      0      0      0      0       0      0       0
3              0       0      0      0      0      0       0      0       0
4              0       0      0      0      0      0       0      0       0
5              0       0      0      0      0      0       0      0       0
Angle     0    10    20    30    40    50    60    70    80    90 Hemis
Tsol  0.521 0.524 0.517 0.508 0.495 0.472 0.418 0.312 0.153 0.000 0.439
Abs1  0.022 0.022 0.023 0.023 0.025 0.026 0.027 0.029 0.031 0.000 0.025
Abs2  0.102 0.104 0.112 0.117 0.119 0.123 0.135 0.142 0.105 0.000 0.121
Abs3      0     0     0     0     0     0     0     0     0     0     0
Abs4      0     0     0     0     0     0     0     0     0     0     0
Abs5      0     0     0     0     0     0     0     0     0     0     0
Abs6      0     0     0     0     0     0     0     0     0     0     0
Rfsol 0.355 0.350 0.349 0.352 0.361 0.379 0.420 0.517 0.711 1.000 0.404
Rbsol 0.295 0.289 0.287 0.290 0.299 0.316 0.350 0.430 0.616 0.999 0.337
Tvis  0.782 0.787 0.776 0.763 0.744 0.705 0.618 0.450 0.212 0.000 0.655
Rfvis 0.131 0.124 0.123 0.127 0.142 0.173 0.239 0.388 0.664 1.000 0.214
Rbvis 0.138 0.131 0.128 0.131 0.144 0.169 0.218 0.325 0.551 0.999 0.198
SHGC  0.609 0.613 0.613 0.609 0.598 0.578 0.534 0.435 0.244 0.000 0.544
SC: 0.60
Layer ID#         4054     7202        0        0        0        0
Tir              0.000    0.000        0        0        0        0
Emis F           0.840    0.040        0        0        0        0
Emis B           0.840    0.840        0        0        0        0
Thickness(mm)      4.0      4.0        0        0        0        0
Cond(W/m2-C     ) 225.0    225.0        0        0        0        0
Spectral File     None     None     None     None     None     None
Overall and Center of Glass Ig U-values (W/m2-C)
Outdoor Temperature                 -17.8 C      15.6 C      26.7 C      37.8 C
Solar      WdSpd  hcout hrout  hin
(W/m2)     (m/s)     (W/m2-C)
0        0.00  12.25  3.23  7.55  1.32 1.32  1.05 1.05  1.07 1.07  1.16 1.16
0        6.71  25.47  3.21  7.57  1.39 1.39  1.08 1.08  1.10 1.10  1.20 1.20
783        0.00  12.25  3.28  6.91  1.38 1.38  1.15 1.15  1.13 1.13  1.16 1.16
783        6.71  25.47  3.23  6.66  1.45 1.45  1.20 1.20  1.16 1.16  1.19 1.19
*** END OF LIBRARY ***
***************************************************************************************************
*WinID   Description                              Design         U-Value g-value T-sol Rf-sol T-vis
***************************************************************************************************
 10001   Keine Glasscheibe = offen                0.001            5.68  1  1  0  1
 13002   Saint Gobain CLIMAPLUS FUTUR AR 1.1  4/15/4  4/15/4           1.1  0.609  0.521  0.355  0.782
_EXTENSION_WINPOOL_END_




More information about the TRNSYS-users mailing list