Nguan,
  Two things occur to me. First, if you take the max of each zone and 
then sum them, you will probably get a higher value than if you had 
summed the cooling load of the zones, then taken the max. In the first 
case, if all of your zone's have their max cooling load at different 
times then you can get away with putting in a smaller cooling system 
because it will never have to serve all zones at the same time with 
their maximum requirement. Second, the QCOOL that you are getting from 
Type56 is sensible cooling only. It doesn't account for any latent 
cooling that might have to be done as well and therefore does not 
represent the total cooling. If you are doing latent cooling, you will 
need to activate the "dehumidification" in TRNBuild as well as cooling. 
Be a bit careful, however, dehumidification and cooling are treated 
completely separately from one another; you can have cooling without 
dehumidification and dehumidification without cooling.
Kind regards,
 David


#TEO NGUAN TECK# wrote:
> Hi ALL,
>
>  
>
> I would like to use TRNSYS to calculate the cooling load of my 
> building model (altogether 8 zones), instead of traditional methods. I 
> have carried out the following steps and would like to know if I am 
> correct:
>
>  
>
> 1)      I used the cooling available in TRNBuild and set the Room 
> Temperature Control to 25 deg C (unlimited power).
>
> 2)      I retrieved the data (QCOOL) and determine the max QCool 
> required for each zone (by sorting the data using excel).
>
> 3)      I subsequently summed all the maximum QCool from the 8 zones.
>
>  
>
> The final value (ie from step 3) will be used to determine the cooling 
> capacity of my equipment (which is a chilled water cooling system).
>
>  
>
> Are my steps correct? Or can anyone provide me a better approach?
>
>  
>
> Any help is deeply appreciated!
>
>  
>
> Nguan Teck
>
> Undergrad
>
> Nanyang Technological University, Singapore
>
> ------------------------------------------------------------------------
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
>   

-- 
***********************************************************************
Thermal Energy System Specialists (TESS), LLC 
David BRADLEY                      22 N. Carroll Street - Suite 370 
Partner                            Madison, WI 53703 
                                   USA
P: +1.608.274.2577 
F: +1.608.278.1475
E-mail: bradley at tess-inc.com 
Web Pages:  http://www.tess-inc.com    and      http://www.trnsys.com

***********************************************************************

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20081218/39f7c29e/attachment-0005.htm>


More information about the TRNSYS-users mailing list