Bing,
  I would recommend that you look at the building tutorial that is in 
the 06-MultizoneBuilding manual and that you look at the restaurant 
example that you will find in the ..\Trnsys16_1\Examples\ directory. The 
TRNSYS building model doesn't care about the shape of walls, only about 
their areas and orientations. Orientations are defined in two parts. 
They are given a name in TRNBuild. Each orientation name defined in 
TRNBuild becomes a set of inputs to the building model. It is then 
necessary to define the slope and azimuth in the weather data reader / 
processor (Type15 or Type109) and connect the appropriate outputs to the 
building model's inputs.
Kind regards,
 David


Bing Dong wrote:
> Hey there
>
> I'm new to Trnsys. I have a question.
>
> Can trnsys do any shape of geometry such as a triangle shape wall with 
> any degree of wall orientation?
>
> Because from the TRNSYS build input, I can only specify wall 
> orientation such as Northwest etc..without any degrees
>
> Thanks,
>
> Bing
> ------------------------------------------------------------------------
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
>   

-- 
***********************************************************************
Thermal Energy System Specialists (TESS), LLC 
David BRADLEY                      22 N. Carroll Street - Suite 370 
Partner                            Madison, WI 53703 
                                   USA
P: +1.608.274.2577 
F: +1.608.278.1475
E-mail: bradley at tess-inc.com 
Web Pages:  http://www.tess-inc.com    and      http://www.trnsys.com

***********************************************************************

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20081216/0140a020/attachment-0005.htm>


More information about the TRNSYS-users mailing list