Julie,
I would recommend looking at some of Type56's energy balance outputs.
Your calculation ignores the energy that is being stored in the wall at
any given time, which can significantly throw off your energy balance.
Kind regards,
David
Julien L'Hoest wrote:
> Dear all,
>
> I just have a little question about the Transmission losses calculated
> by type 56, the Q_UA output exactly.
>
> I use a kind of static model of a building to determine boiler/chiller
> power in winter/summer. Here are the results:
>
> during winter:
> T_out = -12
> T_in = 21
>
> Transmission losses (Q_UA) = 166 kW
>
> During summer:
> T_out = 32
> T_in = 26
>
> Transmission losses = -3 kW
>
> I thougt Q_UA should be proportionnal to Delta T and then equal to
> about -30 kW during summer. Does someone know how the Q_UA output is
> calculated ? Is there any other output that I could use to make a
> static energy balance instead of Q_UA ?
>
> Kind regards.
>
> Julie L.
>
> ------------------------------------------------------------------------
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
>
--
***********************************************************************
Thermal Energy System Specialists (TESS), LLC
David BRADLEY 22 N. Carroll Street - Suite 370
Partner Madison, WI 53703
USA
P: +1.608.274.2577
F: +1.608.278.1475
E-mail: bradley at tess-inc.com
Web Pages: http://www.tess-inc.com and http://www.trnsys.com
***********************************************************************
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20081202/f27db570/attachment-0001.htm>
More information about the TRNSYS-users
mailing list