[TRNSYS-users] problem with building-equipment
knut.erik.enerstvedt at niva.no
knut.erik.enerstvedt at niva.no
Thu Aug 28 23:47:42 PDT 2008
Hello Laura,
I have looked at your project, and see that you have connected the air flow
rate (in kg/hr) from the heat pump directly to the building. The air change
input to the building zones must be in (kg/hr air from heat pump)/(kg air
in zone), so that the unit is 1/h. Put an equation between the heat pump
and the building to do this. Although I have not tried to do these changes
to your project, I think that this must be the error.
Kind regards,
Knut Erik
trnsys-users-requ
est at cae.wisc.edu
To
27.08.2008 19:37 trnsys-users at cae.wisc.edu
cc
Please respond to Subject
trnsys-users at cae. TRNSYS-users Digest, Vol 44, Issue
wisc.edu 22
----- Message from "latara\@libero\.it" <latara at libero.it> on Wed, 27 Aug
2008 19:18:03 +0200 -----
To: "trnsys-users\@cae\.wisc\.edu" <trnsys-users at cae.wisc.edu>
Subject: [TRNSYS-users] problem with building-equipment
Hello,my name is Laura. I have a problem with my thesis.I don't understand
because I get strange results in my simulation.The internal temperature in
building must be 24-26°C, but I get 8-10°C with heat pump. Why? Where is
the error? I send you my file, please help me.
Thank you in advance.
(See attached file: edificioconimpiantodefinitivoestivo.TPF)(See attached
file: Wizard6conimpianto.bui)(See attached file: IT-Brindisi-163200.tm2)
_______________________________________________
----------------------------------------------------------------------------------------------------------------------
NIVAs hovedkontor har flyttet til nye lokaler i CIENS - Forskningssenter
for miljø og samfunn; Gaustadalléen 21, 0349 Oslo. Meld deg på vårt
nyhetsbrev på www.niva.no
-------------- next part --------------
A non-text attachment was scrubbed...
Name: edificioconimpiantodefinitivoestivo.TPF
Type: application/octet-stream
Size: 207191 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20080829/8b5e4cca/attachment-0015.obj>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Wizard6conimpianto.bui
Type: application/octet-stream
Size: 40300 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20080829/8b5e4cca/attachment-0016.obj>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: IT-Brindisi-163200.tm2
Type: application/octet-stream
Size: 1261501 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20080829/8b5e4cca/attachment-0017.obj>
More information about the TRNSYS-users
mailing list