[TRNSYS-users] Some questions on the design of a tank
Jeff Thornton
thornton at tess-inc.com
Fri Aug 15 09:14:46 PDT 2008
<For these I needed 3 inputs and 3 outputs but the tank from the library
has 2 inputs and 2 outputs maximum.>
Tatiana,
If two of the three ports that you need have the same inlet and outlet
locations (both in the bottom and out the top for example) then you can
use a set of mixing and diverter valves to mimic three ports in the tank.
Otherwise the TESS 534 storage tank and the TRANSSOLAR storage tank (which
are both add-ons to TRNSYS) allow the user to have more than two
inet/outlet combinations.
Jeff
Jeff Thornton
President - TESS, LLC
2916 Marketplace Drive - Suite 104
Madison WI 53719 USA
Phone: 608-274-2577
Fax: 608-278-1475
E-mail: thornton at tess-inc.com
Web: www.tess-inc.com
More information about the TRNSYS-users
mailing list