[TRNSYS-users] Double glazing ventilated facade
Technical Support
TechSupport at tess-inc.com
Fri Apr 18 08:41:13 PDT 2008
I would recommend that you treat the facade space as a zone in Type56. You then have some choices as to how you model the ventilation. If the facade is mechanically ventilated, you can simply define a ventilation type in TRNBuild and attach a fan to it. If the facade space is naturally ventilated then there is a rather simplistic equation given in the ASRHAE Fundamentals (2005) chapter 27 that you can use. A much better (but a good bit more complex) solution would be to use either CONTAM and Type97, COMIS 3.2, or TRNFLOW to calculate the air flow through the facade.
Kind regards,
David
Technical Support TeamThermal Energy System Specialists, LLC2916 Marketplace Dr, Suite 104Madison, WI 53719techsupport at tess-inc.com
----- Original Message -----
Subject: [TRNSYS-users] Double glazing ventilated facade
From: Κώστας Ορδουμποζάνης >;kordou at gmail.com>
Date: Thu, April 17, 2008 8:26
Hi! I am trying to model a double glazed ventilated facade, but I don't know how..
Any help would be usefull
Thank you