Chun Kwong,
   Convergnce problems are a result of one of two things usually. 
Either there is not enough thermal capacitance in a given flow loop 
(such as a piping network) or the time step is too big. If I recall, 
your simulation was using a 1 hour time step. I would recommend 
starting by reducing that time step to 0.125 hours to see if that 
solves the convergence problems. The bore field and the building in 
your system should be providing adequate thermal capacitance.
Kind regards,
  David


At 21:17 5/21/2007, h8304506 at hkusua.hku.hk wrote:
>Dear all.
>
>I am simulating a GSHP system, but receive warnings that some units do
>not converge at particular time steps.  The simulation stops after the
>number of warnings reach a limit.  I try to adjust the minimum
>relaxation factor and tolerance of convergence in the control card,
>but it seems to have no improvement.  Please advise how I can fix it?
>Thank you!
>
>Yours sincerely,
>LEE, Chun Kwong
>PhD student
>Department of Mechanical Engineering
>University of Hong Kong
>
>
>
>
>_______________________________________________
>TRNSYS-users mailing list
>TRNSYS-users at engr.wisc.edu
>https://www.cae.wisc.edu/mailman/listinfo/trnsys-users

****************************************************************************************
Thermal Energy System Specialists (TESS), LLC
David BRADLEY                           2916 Marketplace Drive - Suite 104
Partner                                        Madison, WI 53719
Phone: (608) 274-2577 USA
Fax: (608) 278-1475
E-mail: bradley at tess-inc.com
Web Pages:  http://www.tess-inc.com     and      http://www.trnsys.com

"Providing software solutions for today's energy engineering projects"
****************************************************************************************





More information about the TRNSYS-users mailing list