[TRNSYS-users] Problem with an input
David Bradley
bradley at tess-inc.com
Tue May 15 07:03:16 PDT 2007
Samir,
The error is because your entering dry bulb temperature (connected
from Type109 ambient temperature) is less than your entering wet bulb
temperature (set to a constant value of 22C) at time 1 of your
simulation. Since wet bulb temperature is not a direct output of
Type109, you need to connect both dry and wet bulb temperature from
the component labeled "psychrometrics" to the cooling coil.
Cheers,
David
At 06:30 5/15/2007, Chehal, Samir wrote:
>Dear Trnsys users,
>
>I have a problem with my connection: input 1 of "Batt froide CTA
>hbgt so" is not correct and I don't know why.
>
>The message error is:
>
>*** Fatal Error at time : 1.000000
>
> Generated by Unit : 17
>
> Generated by Type : 32
>
> TRNSYS Message 103 : The TRNSYS TYPE checking routine has
> found an inconsistency in the specified component between the input
> file and the information expected by the Type
>
> Reported information : An illegal INPUT value has been
> reported by the model. The model has reported that Input 1 is the
> problem - but this may not be the case. Please check the component
> configuration.
>
><<Wizard25.tpf>>
>
>Best Regards
>=========================================================
>
>NOTICE - This communication may contain confidential and privileged
>information that is for the sole use of the intended recipient. Any viewing,
>copying or distribution of, or reliance on this message by unintended
>recipients is strictly prohibited. If you have received this message in
>error, please notify us immediately by replying to the message and deleting
>it from your computer.
>
>=========================================================
>_______________________________________________
>TRNSYS-users mailing list
>TRNSYS-users at engr.wisc.edu
>https://www.cae.wisc.edu/mailman/listinfo/trnsys-users
****************************************************************************************
Thermal Energy System Specialists (TESS), LLC
David BRADLEY 2916 Marketplace Drive - Suite 104
Partner Madison, WI 53719
Phone: (608) 274-2577 USA
Fax: (608) 278-1475
E-mail: bradley at tess-inc.com
Web Pages: http://www.tess-inc.com and http://www.trnsys.com
"Providing software solutions for today's energy engineering projects"
****************************************************************************************
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20070515/91ee27f2/attachment-0005.htm>
More information about the TRNSYS-users
mailing list