[TRNSYS-users] Error in simulating GSHP system

David Bradley bradley at tess-inc.com
Mon May 14 14:16:25 PDT 2007


Chun Kwong,
   Your data reader is only set to read two columns from each line of 
your data file but you have connected outputs 1 through 6 to other 
components in your system. You need to set parameter 2 to a value of 6.
Cheers,
  David


At 02:04 5/14/2007, h8304506 at hkusua.hku.hk wrote:
>Dear all,
>
>I am simulating a GSHP system, but with error found (please see
>attached files).  Can anyone give me some advice?
>
>Yours sincerely,
>LEE, Chun Kwong
>PhD student
>Department of Mechanical Engineering
>University of Hong Kong
>
>
>
>
>_______________________________________________
>TRNSYS-users mailing list
>TRNSYS-users at engr.wisc.edu
>https://www.cae.wisc.edu/mailman/listinfo/trnsys-users

****************************************************************************************
Thermal Energy System Specialists (TESS), LLC
David BRADLEY                           2916 Marketplace Drive - Suite 104
Partner                                        Madison, WI 53719
Phone: (608) 274-2577 USA
Fax: (608) 278-1475
E-mail: bradley at tess-inc.com
Web Pages:  http://www.tess-inc.com     and      http://www.trnsys.com

"Providing software solutions for today's energy engineering projects"
****************************************************************************************





More information about the TRNSYS-users mailing list