Dear Samir,

I have tried to connect the both components, and it works fine. I have 
certainly not connect the appropriate outputs from equation window to 
Type32 inputs.

The problem comes from the definition of your variables in eqaution 
window : many variables are used both in "Debit" equation window aand in 
"Shading + Light" Equation window. You can't define the same variable at 
several places : all variables names must be unique, so rename variable 
in equation window...

I think you have made a copy/paste of one equation window, so all of 
your variables are defined twice. So you have to supress these variables 
from one equation window.

Best regards, Adrien

Chehal, Samir a écrit :
>
> Dear Trnsys users,
>
> I can’t connect equation with another type and I don’t know why.
>
> In this example I try to connect “Debit” with “Batt froide CTA hbgtso” 
> but I can not.
>
> Best Regards <<Wizard25.tpf>>
>
> =========================================================
>
> NOTICE - This communication may contain confidential and privileged
> information that is for the sole use of the intended recipient. Any 
> viewing,
> copying or distribution of, or reliance on this message by unintended
> recipients is strictly prohibited. If you have received this message in
> error, please notify us immediately by replying to the message and 
> deleting
> it from your computer.
>
> =========================================================
> ------------------------------------------------------------------------
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at engr.wisc.edu
> https://www.cae.wisc.edu/mailman/listinfo/trnsys-users
>   

-- 

***************************************************************
Adrien JEZEQUEL	
Ingénieur en Simulations Dynamiques
ITF (Ingénierie Tous Fluides)
87, route de Chambéry
73230 ST ALBAN EN LEYSSE
FRANCE
Tel: 04.79.75.00.29
Website: www.itf.biz
Mail : a.jezequel at itf.biz





More information about the TRNSYS-users mailing list