Angela,
  In TRNBuild, you need to click on the "Outputs" button in the main 
project overview window then click the "Add" button in the window 
that pops up. Select the zones for which you want to see relative 
humidity (or other outputs) and then select RELHUM (NTYPE 8) from the 
list in the lower right hand side of the window and move it across to 
the list on the left. For a complete list of available NTypes, please 
refer to the Type56 documentation in the 06-MultizoneBuilding manual.
Kind regards,
  David


At 18:53 5/3/2007, Angela Marcela Fandino Sepulveda wrote:
>Dear Mr Bradley
>
>I am using TRNSYS - Type 56a and I am getting the following external files:
>" Bldg-Monthly.out, Bldg-HourlyTemp.out, Bldg-HourlyLoads.out "
>I would like also to obtain relative humidity hourly.
>I was wondering if I have to change the source code for Type56 or if I can
>obtain them in any other way.
>I really appreciate your kind assistance,
>Regards,
>Angela
>
>
>
>--
>Angela Fandino
>Department of Civil and Environmental Engineering,
>The University of Melbourne, Australia
>Tel: +61 3 8344 4291,
>M: 0430 105 302
>email: a.fandinosepulveda at pgrad.unimelb.edu.au
>URLs: http://www.civenv.unimelb.edu.au/autohome/webpage.php3?login=angelaf
>
>_______________________________________________
>TRNSYS-users mailing list
>TRNSYS-users at engr.wisc.edu
>https://www.cae.wisc.edu/mailman/listinfo/trnsys-users

****************************************************************************************
Thermal Energy System Specialists (TESS), LLC
David BRADLEY                           2916 Marketplace Drive - Suite 104
Partner                                        Madison, WI 53719
Phone: (608) 274-2577 USA
Fax: (608) 278-1475
E-mail: bradley at tess-inc.com
Web Pages:  http://www.tess-inc.com     and      http://www.trnsys.com

"Providing software solutions for today's energy engineering projects"
****************************************************************************************





More information about the TRNSYS-users mailing list