[TRNSYS-users] Tsky calculation with 2 different Types: Big difference in results!!!
David Bradley
bradley at tess-inc.com
Tue May 15 08:21:52 PDT 2007
Talal,
Type69 allows you to use two different sky
temperature algorithms; in one, the cloudiness
factor is read as an input while in the other, it
is calculated internally based on ambient
conditions (temperature, humidity, and solar
radiation). Type15 and Type69a use the same
algorithm. Type15 and Type69b do not. You can
look at matched results between Type15 and
Type69a but unfortunately, you cannot use Type109
as the weather component because it does not
read, process, or output the cloudiness factor.
You need to use the combination of Types 89 and 16 instead.
In looking at your project, I noticed a couple of other things as well.
First, and most importantly, when you change the
units of an input, that change only affects the
value of unconnected inputs. As soon as you
connect the output of another component to the
input, information is passed directly and without
conversion. It looks as though you changed the
input of Type33 to pascals so that you could
directly pass the atmospheric pressure output of
Type109 (which is in pascals). You need to leave
the Type33 input units as atmospheres and you
need to put an equation into your input file to
convert Type109's outputs from Pa to atm.
Second, the elevation parameter in Type69 was set
to 0 and should be set to 240m as the elevation
of Lyon. You can read the elevation from the first line of the *.tm2 file.
Third, the wet bulb temperature calculated by
Type15 and Type33 are different because Type33
was set to "wet bulb calculation mode" 0 (do not
calculate the wet bulb temperature).
Cheers,
David
At 08:38 5/15/2007, Talal SALEM wrote:
>Dear fellows,
>
>I have a question concerning the calculation of the effective Sky Temperature.
>When I use on the one hand the Type 15-6, and on
>the other hand a combination of Type 109 with
>the Type 69b and the Type33e, the results of the
>effective sky temperature differs although in
>the mathematical reference we can see that the
>same equations are used for both cases (Tsky in
>Type15-6, and Tsky in Type 33) in the
>calculation. [Please check attached Trnsys file]
>Can you please check this big difference (up to 10°c)?
>Thank you in advance
>
>Talal S.
>
>
>_______________________________________________
>TRNSYS-users mailing list
>TRNSYS-users at engr.wisc.edu
>https://www.cae.wisc.edu/mailman/listinfo/trnsys-users
****************************************************************************************
Thermal Energy System Specialists (TESS), LLC
David BRADLEY 2916 Marketplace Drive - Suite 104
Partner Madison, WI 53719
Phone: (608) 274-2577 USA
Fax: (608) 278-1475
E-mail: bradley at tess-inc.com
Web Pages: http://www.tess-inc.com and http://www.trnsys.com
"Providing software solutions for today's energy engineering projects"
****************************************************************************************
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20070515/2b24668f/attachment-0001.htm>
More information about the TRNSYS-users
mailing list