[TRNSYS-users] Error in simulating GSHP system

David Bradley bradley at tess-inc.com
Mon May 14 14:16:25 PDT 2007


Chun Kwong,
   Your data reader is only set to read two columns from each line of 
your data file but you have connected outputs 1 through 6 to other 
components in your system. You need to set parameter 2 to a value of 6.
Cheers,
  David


At 02:04 5/14/2007, h8304506 at hkusua.hku.hk wrote:
>Dear all,
>
>I am simulating a GSHP system, but with error found (please see
>attached files).  Can anyone give me some advice?
>
>Yours sincerely,