[TRNSYS-users] controller type 2
David Bradley
bradley at tess-inc.com
Thu May 10 08:06:55 PDT 2007
Betrand,
I think you are going to need to use two
controllers. The first controller will determine
the flow rate of your collector loop in order to
maintain a collector outlet temperature of 70C.
The other controller will determine the flow rate
on the load side of your heat exchanger in order
to maintain source side outlet temperature of
60C. I am also not sure that Type2 is an
appropriate controller model; Type2 models a
differential controller that has only two states:
ON and OFF. In order to modulate your flow and
maintain an outlet temperature, you will need to
use a proportional or a PID controller. There are
some solar collector models in the TESS Solar
Library that combine a variable speed pump,
controller, and collector and modulate the
required inlet flow rate in order to maintain an outlet temperature.
Kind regards,
David
At 01:50 5/10/2007, tchanche fankam bertrand wrote:
>Dear all,
>i am simulating a system that comprises a
>subsystem made of a colector loop(ETC collector,
>pump, flat plate heat exchanger ). i need to to
>keep the inlet temperature of the collector at
>60C and the outlet temperature at 70C.
>I would like to know if it is possible to
>control the system with type 2 and how.
>Thank in advance for your help.
>yours,
>
>
>------------------------
>TCHANCHE FANKAM Bertrand
>
>C/O SUH Christopher
>22 kadmeas-BOTANIKOS
>11855 Athens, GREECE
>mobile:+30 694 295 5952
>office: +30 210 529 4046
>
>
>Découvrez une nouvelle façon d'obtenir des
>réponses à toutes vos questions ! Profitez des
>connaissances, des opinions et des expériences
>des internautes sur
><http://fr.rd.yahoo.com/evt=42054/*http://fr.answers.yahoo.com>Yahoo!
>Questions/Réponses.
>_______________________________________________
>TRNSYS-users mailing list
>TRNSYS-users at engr.wisc.edu
>https://www.cae.wisc.edu/mailman/listinfo/trnsys-users
****************************************************************************************
Thermal Energy System Specialists (TESS), LLC
David BRADLEY 2916 Marketplace Drive - Suite 104
Partner Madison, WI 53719
Phone: (608) 274-2577 USA
Fax: (608) 278-1475
E-mail: bradley at tess-inc.com
Web Pages: http://www.tess-inc.com and http://www.trnsys.com
"Providing software solutions for today's energy engineering projects"
****************************************************************************************
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20070510/340a7895/attachment-0001.htm>
More information about the TRNSYS-users
mailing list