[TRNSYS-users] About schedule
Hermann Schranzhofer
hermann.schranzhofer at tugraz.at
Tue Mar 27 23:11:37 PDT 2007
Generator Microsoft Word 11 (filtered medium) Dear Fabien Morice,
one way is to generate a datafile with the desired schedule and use it as an input file. For example use the tool of your choice (Excel, Matlab, Origin . ) and generate a file with 0 and 1 for each hour you want to switch the ventilation on (1) or off (0):
1.0 0
2.0 0
3.0 0
4.0 0
5.0 0
6.0 0
7.0 1
8.0 1
9.0 1
10.0 1
11.0 1
12.0 1
13.0 1
14.0 1
15.0 1
16.0 1
17.0 0
18.0 0
19.0 0
20.0 0
21.0 0
22.0 0
23.0 0
Usw.
Read in this file in your simulation and connect the output of the data reader (e.g. Type9) with the input you defined in your building (type56). Then you can use this value in TRNBUILD in the ventilation input with the equation 1 * Schedule + 0. Of course you can adapted this routine to your requirements.
I hope it helps and good luck
Hermann Schranzhofer.
_______________________________________________________________DI Dr. mont. Hermann SchranzhoferInstitut fuer Waermetechnik / Institute of Thermal EngineeringTU Graz / Graz University of Technology Inffeldgasse 25 / B, A-8010 GrazTel.: +43 316 873 7314Fax : +43 316 873 7305http://www.iwt.tugraz.at/ _______________________________________________________________
Von: Fabien Morice [mailto:fabien.morice at yahoo.fr] Gesendet: Dienstag, 27. März 2007 17:15 An: trnsys-users at engr.wisc.edu Betreff: [TRNSYS-users] About schedule
Dear TRNSYS users, I havea question for you :
Do you know how I can simulate a year-schedule ? I would like to simulate school-holiday during all the year ?
In more, I would like to preserve week-schedule and day-schedule.
Is itpossible ?
I need this schedule for the :
- internal gains
- lighting
- ventilation ...
Fabien Morice.
Découvrez une nouvelle façon d'obtenir des réponses à toutes vos questions ! Profitez des connaissances, des opinions et des expériences des internautes sur Yahoo! Questions/Réponses.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20070328/4fa2b65a/attachment-0005.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Hermann Schranzhofer.vcf
Type: application/octet-stream
Size: 208 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20070328/4fa2b65a/attachment-0005.obj>
More information about the TRNSYS-users
mailing list