Concerning my precedent mail, i haven't seen that the air flow
temperature was equal to outside temperature from 0h to 9h and from 18h 24h!
In that way, you just have to define one Forcing Function which is 1
from 9 to 18h. This forcing function will be connected to Input1 for
Equation Window.
Then, in equation window, define ouput like below :
Output = 23*Input1 + Text*NOT(Input1)
Since NOT(Input1) =
- 0 when Input1 (Forcing Function) = 1
- 1 when Input1 (Forcing Function) = 0
Sorry for the desagrement,
Best regards Adrien
Chehal, Samir a écrit :
>
> Dear all,
>
> I must insert new equation to define a temperature of air flow.
>
> The schedule of temperature air flow is:
>
> 23°C between 9h and 18h
>
> outside temperature between 0h and 9h , and between 18h and 24h
>
> and this during the entire year.
>
> I would know what function allow this scenario and what represent
> different functions (GE,NE,MIN,MOD,….) and how I must use them.
>
> _NB_: I defined air flow temperature like an input in TRNBUILD.
>
> Best regards.
>
> =========================================================
>
> NOTICE - This communication may contain confidential and privileged
> information that is for the sole use of the intended recipient. Any
> viewing,
> copying or distribution of, or reliance on this message by unintended
> recipients is strictly prohibited. If you have received this message in
> error, please notify us immediately by replying to the message and
> deleting
> it from your computer.
>
> =========================================================
> ------------------------------------------------------------------------
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at engr.wisc.edu
> https://www.cae.wisc.edu/mailman/listinfo/trnsys-users
>
--
***************************************************************
Adrien JEZEQUEL
ITF (Ingénierie Tous Fluides)
87, route de Chambéry
73230 ST ALBAN EN LEYSSE
FRANCE
Tel: 04.79.75.00.29
Website: www.itf.biz
Mail : a.jezequel at itf.biz
More information about the TRNSYS-users
mailing list