Fabien,
If you have horizontal insulation directly underneath the entire slab
then you would define that insulation in TRNBuild as a layer in the
BOUNDARY wall that defines the slab. If you have insulation that extends
vertically downward around the perimeter of the slab (like a skirt) then
you define its R-value and the depth to which it extends using parameters
17 and 18 of Type703. If you have horizontal insulation that extends
outward from the perimeter of the slab or if you have horizontal insulation
that extends inward from the perimeter but does not extend all the way to
the middle of the slab then the effects of that kind of insulation is not
calculated by Type703. If I am misunderstanding the type of insulation that
you are considering, my apologies. Please feel free to send me a sketch of
what you are trying to analyze and I will try to answer more clearly.
Cheers,
David
At 11:36 3/27/2007, Fabien MELENEC wrote:
>Dear TRNSYS users,
>
>I am using the Type703 (slab on grade) and would like to know if this
>component is able to take in consideration horizontal perimeter insulation.
>
>Best regards
>
>Fabien MELENEC
>Email : <mailto:fabien.melenec at addenda.fr>fabien.melenec at addenda.fr
>
>Sté ADDENDA
>Service administratif et direction
>RN d'Auch
>32300 MIRANDE
>
>_______________________________________________
>TRNSYS-users mailing list
>TRNSYS-users at engr.wisc.edu
>https://www.cae.wisc.edu/mailman/listinfo/trnsys-users
****************************************************************************************
Thermal Energy System Specialists (TESS), LLC
David BRADLEY 2916 Marketplace Drive - Suite 104
Partner Madison, WI 53719
Phone: (608) 274-2577 USA
Fax: (608) 278-1475
E-mail: bradley at tess-inc.com
Web Pages: http://www.tess-inc.com and http://www.trnsys.com
"Providing software solutions for today's energy engineering projects"
****************************************************************************************
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20070330/0b454b8e/attachment-0001.htm>
More information about the TRNSYS-users
mailing list