Hi Fredery,
If I understand correctly, you have a problem with cycling information
that is getting in to an infinite loop.
One solution is to add some inertia to your system. You did not specify
if you have a Type56 in your simulation, or another load. You may want
to add a pipe (Hydronids/Pipe_duct/type31), which adds some inertia to
the system.
Another solution is to use an input value recall
(Utility/InputValueRecall/Type93): you can set it up so it keeps track
of the value of a variable during previous time steps; this is an
artificial way of adding inertia to your system. If you try out this
solution, please run a sensitivity analysis with the time step to make
sure that you are getting appropriate solutions, and that energy is
being conserved in your system.
Best regards,
Diego
fredery lavoye wrote:
> Hi
> I try to simulate a heating by ventilation. To know the temperature I
> want to use for the heating at a timestep, I need the Qheat at this
> time step. So I do an iteration with type 155; while Qheat is
> different to zero make (T+0.1). But the simulation doesn't
> converge!It's due to the Qheat which linked to the ventilation.
> How can I solve this problem?
> Please help me.
> Best regards,
> Fredery.
>
> ------------------------------------------------------------------------
> Avec Windows Live Spaces, publiez directement des messages
> électroniques sur votre blog ou ajoutez-y des photos, des blagues et
> d'autres infos. C'est gratuit !
> <http://clk.atdmt.com/MSN/go/msnnksac0030000001msn/direct/01/?href=http://www.imagine-msn.com/spaces>
>
> ------------------------------------------------------------------------
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at engr.wisc.edu
> https://www.cae.wisc.edu/mailman/listinfo/trnsys-users
>
--
Diego A. Arias
TRNSYS Coordinator
Solar Energy Laboratory
University of Wisconsin - Madison
1500 Engineering Drive
Madison, WI 53706
More information about the TRNSYS-users
mailing list