[TRNSYS-users] some problems found with the type92 in Trnsys16
Yujun TAO
aleck1314 at yahoo.fr
Tue Jul 10 02:00:13 PDT 2007
Hello,
I found some problems with the type92 in Trnsys16. I checked the program *.for
One problem is located here :
PERFORM INITIAL TIMESTEP MANIPULATIONS
...
!check the parameters for problems and RETURN if any are found
...
IF((HTREFF.LT.0.).OR.(HTREFF.LT.1.)) CALL TYPECK(-4,INFO,0,4,0)
Well, the second comparison in the parentheses of IF is wrong, it should be H(TREFF.GT.1).
The other problems are located below the ligne of nomber 20. For the calcul of QAUX and QLOSS. Firstly, let's look at them:
QAUX = (FLOW*CP*(TIN-TOUT)+UA*(TBAR-TAMB))/HTREFF,
QLOSS = UA*(TBAR-TAMB) + (1.d0-HTREFF)*QAUX
Generaly, the environmental temperature is higher than the average temperature of a chilled fluide, so TBAR-TAMB is less than 0, so for a electrical compressed chiller, it should take more chaleur. There is an impression that the ambiante give the chaleur to the fluide. Finally, the two fomulas shoud be like this:
QAUX = (FLOW*CP*(TIN-TOUT)+UA*(TAMB-TBAR))/HTREFF
QLOSS = (1.d0-HTREFF)*QAUX
That's all.
Aleck (France)
_____________________________________________________________________________
Ne gardez plus qu'une seule adresse mail ! Copiez vos mails vers Yahoo! Mail
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20070710/df416497/attachment-0001.htm>
More information about the TRNSYS-users
mailing list