Gizmoog,
I would recommend using either a Type14 forcing function in combination
with a controller component (Type2 for example) to turn on and off the
chiller. Type2 would operate the chiller based only on Type56 zone
temperatures regardless of the time of year. Type14 would be set up to
disable the controller during the winter months so that the chiller remains
off. To do this, your Type14 forcing function might have a value of 1
during the summer and 0 during the winter and you might multiply the value
of the forcing function by the control signal coming from Type2. If you
have access to the TESS Applications Library, there is a heating and
cooling season component that will do the same basic thing in a bit more
comprehensible way.
Kind regards,
David
At 12:12 1/4/2007, gizmoog wrote:
>Hello,
>
>I'm new in Trnsys and I'd like to use Type 56 to model a building zone
>but I don't know how to tell that the chiller (for example, could be the
>same problem with a heating) is
>working only during the summer.
>Actually, I have only a week schedule I didn't find where I can precise
>that this week description is only for july and august for example.
>
>Can someone help me ?
>
>best regards,
>gizmoog
>
>
>_______________________________________________
>TRNSYS-users mailing list
>TRNSYS-users at engr.wisc.edu
>https://www.cae.wisc.edu/mailman/listinfo/trnsys-users
****************************************************************************************
Thermal Energy System Specialists (TESS), LLC
David BRADLEY 2916 Marketplace Drive - Suite 104
Partner Madison, WI 53719
Phone: (608) 274-2577 USA
Fax: (608) 278-1475
E-mail: bradley at tess-inc.com
Web Pages: http://www.tess-inc.com and http://www.trnsys.com
"Providing software solutions for today's energy engineering projects"
****************************************************************************************
More information about the TRNSYS-users
mailing list