[TRNSYS-users] Type56 - 2 active layers in one wall??
Arie Kalkman
a.kalkman at chri.nl
Thu Feb 8 03:26:13 PST 2007
Hello Björn,
I asked the same question some time ago, and got a direct reply by Marco, so
it's not in the archive. The idea is to insert a dummy zone with a low
thermal resistance between the two active layers. It worked quite well in my
case, thanks Marco. Schematically, it looks like this:
Zone 1
--------------------------------------
oooooooooooooooooooooo active layer1
xxxxxxxxxxxxxxxxxxxxxxxxxxx slab
xxxxxxxxxxxxxxxxxxxxxxxxxxx slab
oooooooooooooooooooooo active layer2
--------------------------------------
Zone 2
Which is modeled as:
Zone 1
--------------------------------------
oooooooooooooooooooooo active layer1
xxxxxxxxxxxxxxxxxxxxxxxxxxx slab
---------------------------------------
Fictive zone
---------------------------------------
xxxxxxxxxxxxxxxxxxxxxxxxxxx slab
oooooooooooooooooooooo active layer2
--------------------------------------
Zone 2
Regards, Arie
-----Oorspronkelijk bericht-----
Van: trnsys-users-bounces at engr.wisc.edu
[mailto:trnsys-users-bounces at engr.wisc.edu] Namens Bjoern Nienborg
Verzonden: donderdag 8 februari 2007 11:40
Aan: trnsys-users at engr.wisc.edu
Onderwerp: [TRNSYS-users] Type56 - 2 active layers in one wall??
Hello together!
I'm trying to simulate a two-storied house with floor heating and
chilled ceiling. This means I need two active layers in the first level
floor. This isn't permitted by Trnbuild. Does anyone have an idea how to
get around this limitation?
Thanks for any help!
Björn
--
Björn Nienborg
Thermal Systems and Buildings
Fraunhofer Institut für Solare Energiesysteme ISE
Heidenhofstr. 2, 79110 Freiburg, Germany
Tel.: +49 (0)761 4588-5528 FAX: +49 (0)761 4588-9000
http://www.ise.fraunhofer.de
_______________________________________________
TRNSYS-users mailing list
TRNSYS-users at engr.wisc.edu
https://www.cae.wisc.edu/mailman/listinfo/trnsys-users
More information about the TRNSYS-users
mailing list