[TRNSYS-users] concrete core cooling modelled with active layer

Arie Kalkman a.kalkman at chri.nl
Tue Feb 6 07:34:07 PST 2007


Dear Oliver,

 

The cooling power also depends on the room temperature. The quoted 40-60
W/m2 is usually specified at peak cooling demand, usually at a
roomtemperature of 25 or 26 C. If the room doesn’t get that hot, the
supplied cooling power is less. Usually, the aim of the concrete cooling
system is to condition the room (which is quite succesfull when 21 C room
temperature is achieved) and not to deliver a large cooling power. However,
when a comparison with other cooling systems is made, the maximum cooling
power is sometimes used. In my opinion, your modeling results show that for
the specific project you don’t need these large cooling powers.

 

Regards, Arie

 

 

 

 

  _____  

Van: trnsys-users-bounces at engr.wisc.edu
[mailto:trnsys-users-bounces at engr.wisc.edu] Namens Pol Olivier
Verzonden: dinsdag 6 februari 2007 15:44
Aan: trnsys-users at engr.wisc.edu
Onderwerp: [TRNSYS-users] concrete core cooling modelled with active layer

 

Dear TRNSYS users,

I am modelling a concrete core cooling (activation of storage mass of slabs)
with an active layer (with TRNSYS 16.01).

Relevant data are:

-          distance to edge of the slab: 12cm

-          pipe spacing: 20cm

-          flow mass: 12kg/h.m²

-          Temperature of supply air into the rooms: 19°C

According to the definition of outputs for a surface, the energy abstracted
from the room into the slab should be QCOMI and QCOMO (considering both
l-wave radiation and convection).

My results are:

-          inlet temperature 19°C, QCOMImax=15W/m²

-          inlet temperature 17°C, QCOMImax=20W/m² (average air temperature
in summer: 21°C)

-          inlet temperature 17°C, without cooling of supply air,
COMImax=25W/m² (average air temperature in summer: 22°C)

The values I obtain for QCOMI and QCOMO are much lower than the ones
obtained in the practice (usually between 40 and 60W/m²).

I tried different variations (simulation time step, distance to the edge of
the slab, flow mass and auto-segmentation, internal calculation of
convective heat transfer coefficient, number of loops) without success


Are QCOMI and QCOMO the right outputs?

Thank you for your suggestions,

Olivier Pol.

 

 

 

____________________________

arsenal research


Geschäftsfeld Nachhaltige Energiesysteme / 
Business Field Sustainable Energy Systems


DI Olivier Pol


Austria, 1210 Vienna, Giefinggasse 2

ph: +43 (0) 50550-6592, f: +43 (0) 50550-6613

mobile: +43 (0)664/ 62 07 890

 <mailto:olivier.pol at arsenal.ac.at> olivier.pol at arsenal.ac.at

 <http://www.arsenal.ac.at/> www.arsenal.ac.at

_________________________

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20070206/2517a2ec/attachment-0005.htm>


More information about the TRNSYS-users mailing list