Hi Jeff,
found something in the source code, that does not match the proforma - see
appendix.
Regards Heinrich
--------------------------------------------------
b+e
Ingenieurbüro
für Bauklima und
Energiekonzeption
Dr. Heinrich Post
Brienner Str. 48
D-80333 München
Fon +49 (0) 89/54320678
Fax +49 (0) 89/54320679
Mobil +49 (0) 160/7225740
mailto:dr.post at ib-bauklima.de
Besuchen Sie uns im Internet:
www.ib-bauklima.de
--------------------------------------------------
-----Ursprüngliche Nachricht-----
Von: info.bauklima [mailto:info at ib-bauklima.de]
Gesendet: Mittwoch, 29. August 2007 11:01
An: 'thornton at tess-inc.com'; 'Heinrich Post'; 'trnsys-users at engr.wisc.edu'
Betreff: AW: [TRNSYS-users] Implementation of TESS-Type 669
Hi Jeff,
There is a mistake in proformo definition - see appendix But why are there
no outputs for energy-values, because of wrong performa definition.
flowrate ist evaluated as pressure I guess.
Does the mistake in the proforma - definition generate zero values for
calculated energy-values ?
Regards
Heinrich
--------------------------------------------------
b+e
Ingenieurbüro
für Bauklima und
Energiekonzeption
Dr. Heinrich Post
Brienner Str. 48
D-80333 München
Fon +49 (0) 89/54320678
Fax +49 (0) 89/54320679
Mobil +49 (0) 160/7225740
mailto:dr.post at ib-bauklima.de
Besuchen Sie uns im Internet:
www.ib-bauklima.de
--------------------------------------------------
-----Ursprüngliche Nachricht-----
Von: Jeff Thornton [mailto:thornton at tess-inc.com]
Gesendet: Mittwoch, 29. August 2007 00:13
An: Heinrich Post; trnsys-users at engr.wisc.edu
Betreff: Re: [TRNSYS-users] Implementation of TESS-Type 669
<I would like to use the TYPE "696b" of the TESS-HVAC-library in my project,
to model the energy-consumption of a simple AC-Unit. But when I checked the
studio example, that I got from TRANSSOLAR , I realized that there is no
possibility to evaluate the energy output of the component.>
The outputs of the model from the proforma should be:
OUT(1)=Outlet air temperature
OUT(2)=Outlet air humidity ratio
OUT(3)=Outlet air percent relative humidity OUT(4)=Outlet air flow rate
OUT(5)=Outlet air pressure OUT(6)=Sensible energy requirement in heating
mode OUT(7)=Latent energy requirement in heating mode OUT(8)=Total
(sensible+latent) energy requirement in cooling mode OUT(9)=Sensible energy
requirement in cooling mode OUT(10)=Latent energy requirement in cooling
mode OUT(11)=Required reheat energy
Please let me know what the outputs are in the proforma that you are using.
Thanks!
Jeff
Jeff Thornton
President - TESS, LLC
2916 Marketplace Drive - Suite 104
Madison WI 53719 USA
Phone: 608-274-2577
Fax: 608-278-1475
E-mail: thornton at tess-inc.com
Web: www.tess-inc.com
_______________________________________________
TRNSYS-users mailing list
TRNSYS-users at engr.wisc.edu
https://www.cae.wisc.edu/mailman/listinfo/trnsys-users
-------------- next part --------------
A non-text attachment was scrubbed...
Name: error_Type_696.gif
Type: image/gif
Size: 18594 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20070829/bb562c4e/attachment-0001.gif>
More information about the TRNSYS-users
mailing list